Search for tools and product advice,

Discuss Lighting circuit - no CPC in the UK Electrical Forum area at ElectriciansForums.net

smity

-
Reaction score
22
Alrite lads,

I'm a commercial spark so don't do much domestic but a mate of mine asked me to Pop round and change a light fitting in his kitchen 5 min job, he had an old 6ft fluorescent which was shot and he has brought a new class 1 fitting.

I remove the fitting and there's no CPC so I checked at the old wylex board and the downstairs lighting has no CPC at all and there's also no RCD present so this is now more than a 5 min job.

I have told him to get a class 2 fitting for the kitchen and advised an RCD/New board but I also think he has some other class 1 fittings which are potentially dangerous (wall lights etc)

So other than remove the class 1 fittings or rewire the circuit is there anything else that can be done?

Thanks
 
think you have answered the question. either install cpc's to lighting or fit classII fittings (and switches)
 
Thanks, Yeah though that but thought I would check incase there was anything else.

Where do I stand on swapping kitchen fitting for class 2 then advising on the remaining work that needs doing if he doesn't have it done? I won't be leaving the circuit more dangerous than it is but not happy that it's potentially dangerous.

And technically I can't change the CU for him as I'm not part p :-(
 
Fit a class 2 fitting and note on a MWC lack of CPC on circuit.

As for DB and part P notification search for a prosecution for failure to notify then see what you think of it.
 
Just another little point,how old is the property? What type of cables are used? I have visited several built in the 60's that were wired in t&e,but had the CPC cut back at every fitting. Cables in good order,IR fine,just required diggin' and extendin' ...
 
Looks like pvc twin with no earth, I managed to pull about 12 inches through and stripped back but still no earth. Not sure on age of the property.
 
Thanks, Yeah though that but thought I would check incase there was anything else.

Where do I stand on swapping kitchen fitting for class 2 then advising on the remaining work that needs doing if he doesn't have it done? I won't be leaving the circuit more dangerous than it is but not happy that it's potentially dangerous.

And technically I can't change the CU for him as I'm not part p :-(

What a load of genitalia, course you can change a CU Part P is a building reg, no one can be part P
 
i can't think of anything pointles or offensive to say so i'll keep schtum.
 
Now that's a novelty!

What's next - pigs with wings???

no wings, i'm afraid... next best thing though....

animals2.jpg
 

Reply to Lighting circuit - no CPC in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
669
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
655
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
732
Just to be clear… I am going to do the correct thing here and pay for the correct parts…. I just wanted to start the discussion. My particular...
Replies
6
Views
312

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock