5,607
Evening all..

I came across an interesting one today that I had not seen before.

I had a simple job of like for like replacement of some ceiling lights. I switched off the lighting circuit but the lights stated on, not too unusual you may think. I then switched off the rest of them one by one and the lights went off with the shower MCB. I then switched the other breakers back on and the lights came back on with the lighting circuit breaker!

I then noticed an unswitched fused spur (in 1mm) from the shower switch which supplied power to the 2 lights I was changing. Then I switched off the shower circuit and noticed that the shower was still live as it was coming through the lighting circuit and then through the 3A fuse!!

Has any one else come across crossed circuits like this? How could it occur? Why would someone do that as the lights already had power so why then give them another source?
 
I've come across multiple lighting circuits wired in conduit that have somehow been interlinked....yes it's funny when trying to find the MCB for the lights you want to isolate only to find none of them do, unless you have both affected circuits off together!
 
Once, installing some extra sockets on a rfc, I had no ring continuity. There was an unused t+e tucked away in the cu.
A bit of investigation and found another unused in the bathroom cylinder cupboard. All 3 were live. I'm sure you can conclude the reason. A good reason for dead testing.....never presume!
 
Sounds very inappropriate but it may have been a DIY attempt to get the lights to come on when the shower was turned on and to have a separate light switch but without realising that the circuits would back feed each other.
At least they fused the lights down but I do not think the fuse would last long with an electric shower running through it! and it was probably lucky the circuit resistances were such that the shower did not pull 3A through the fuse.
 
Came across this too, 9.6kw shower with 1.5 t&e straight out of the shower pull cord
(On a 45a breaker) and into a fuse spur and then on to feed a bathroom fan and 3 downlights. I was wondering why there was no light switch. 1 pull cord does all, some dodgy work
 
Came across this too, 9.6kw shower with 1.5 t&e straight out of the shower pull cord
(On a 45a breaker) and into a fuse spur and then on to feed a bathroom fan and 3 downlights. I was wondering why there was no light switch. 1 pull cord does all, some dodgy work

Unorthodox, but what's wrong with it?
 
So was the shower running off the 1.5mm or just the lighting?
 
Came across this too, 9.6kw shower with 1.5 t&e straight out of the shower pull cord
(On a 45a breaker) and into a fuse spur and then on to feed a bathroom fan and 3 downlights. I was wondering why there was no light switch. 1 pull cord does all, some dodgy work
I had this also once without the fused spur.
 
I've had similar, isolated a shower at DP pull switch to replace and on disconnecting the shower unit found voltage at the neutral. A timer fan had been connected straight off the shower switch with the permanent live on the mains side, more potentially lethal dodgy DIY.
 

Reply to Lights and shower circuit linked together! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just been called out to another burning shower switch.Upon removal the wires had been burnt and chared.One thing I've noticed on all burnt...
Replies
27
Views
1K
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
2K
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
575
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
660
Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock