Ok.......................got a new board change req in a flat in a converted church as they want alot of work done and current board 20 yrs old and cant get rcbo's etc.
the church is on fourth floor, meter and cut out for all flats in basement, all cables run internally when conversion was done.

old tails are 16mm
earth is 10mm

so how do i get round it?

any suggestions?

i.e do i still req to change incoming tails from meter to 25mm and 16mm for earth?
I assume that i would to comply, however this has alot of implications.:confused:
 
Well I'm assuming there is a switchfuse in the basement protecting the circuit??? If not then there should be due to their length.

This makes them a submain circuit rather than meter tails as you are not relying on the DNO fuse for overcurrent protection. Therefore depending on the size of the fuse in the switchfuse, you could run the flat on 2.5 t&e if you wanted.
 
Interesting one this, as i have just done a kitchen where the CU was remote from the intake.

TNS 16mm tails feeding 60A switchfuse and then 16mm T&E s the sub main feed.

Only thing i could do was upgrade MEB.

Although the main earth was undersized, i contacted DNO to make them aware of the situation.

What they do about it is of course another thing.
 
ive just finished a rewire , the CDU was in the kitchen above the kitchen units , so what i have done is run 2 16 mm one to main board one to ECO 7 board used a 3 pole isolator and protected both supplies by a 63 amp mcb and run a seperate earth to each CDU as well as the 6 mm in the 16 mm twe , how ever mine wasnt listed , castles were you ever tride to clip to rock and perished plaster and not being able to drill the rock nightmare
 

Reply to Listed building dilemma! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

We are refurbishing an empty commercial building at the minute and I don't do commercial stuff day in day out so not entirely clued up on...
Replies
11
Views
1K
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
If there isn't a 2-pole isolator there already, I usually get the client to arrange to get one fitted before I do a board change, either through...
Replies
20
Views
3K
Need help with a quote here. I’m wanting some sound advice. Was called out to the hot water not working so repaired the issue within the panel...
Replies
10
Views
1K
Hi I wonder if anyone has any useful thoughts on this. Client wants me to redo consumer unit but doesn’t want disruption to fabric of building...
Replies
27
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock