Search the forum,

Discuss Looking for an easy-to-understand explanation of 3 phase / 3 phase + N in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
70
I have some questions about 3 phase.

1. Does the neutral come in with the supply as standard?
2. As most 3 phase equipment doesn't require an N, what are the circumstances where you need one?
3. When we do need one, why do we need one?
4. Am i right in presuming therefore that we'd mostly use 3c + E as our cable for 3p circuits or would we use a 5c?

Thanks
 
1. Yes

2. There will generally be single phase equipment required, also, if not, much 3 phase equipment these days, requires 230v controls, especially in commercial kitchens, for example.

3. As above.

4. Depends on what the actual circuit requires. Rarely use 5c, mostly 4c swa or singles in conduit, maybe.

Note. This is not an 'easy to understand explanation of 3 phase'.
 
Last edited:
1. Yes

2. There will generally be single phase equipment required, also, if not, much 3 phase equipment these days, requires 230v controls, especially in commercial kitchens, for example.

3. As above, for example.

4. Depends on what the actual circuit requires. Rarely use 5c, mostly 4c swa or singles in conduit, maybe.

Note. This is not an 'easy to understand explanation of 3 phase'.
Thanks. So the 4c SWA will use 3x phase, 1x CPC plus we'll earth the steel wire, is that right?
 
Thanks. So the 4c SWA will use 3x phase, 1x CPC plus we'll earth the steel wire, is that right?

It seems as though you have a specific application in mind and it might be better to provide details.

I'm not long in this industry but, other than for certain loads, haven't yet seen 3 phase distribution without neutral. Generally 4c SWA for L1, L2, L3 & N, with earth provided separately.
 
So what do we do with the neutral most of the time, just leave it floating in a connector?
If you have a 3P & E connector for a load that definitely has no need of neutral, then you would not need to wire it with N to that point, but if it was wired then you would make sure the end was safely isolated. For smaller conductors some would just stick it in to a 2-way Wago terminal or similar so there is no exposed end that might come in contact with anything else.

However, in the more general case you would have 3P+N+E sockets and they must have the neutral connected. Even if your planned load is not needing it, someone in the future might repurpose it and without N and an imbalanced load they would probably damage the appliance.

Simple 3-phase motors do not need N, even if star-connected, but often motor machines using VFD and/or other controls, inspection lights, etc do need N as they are not always a perfectly balanced load and/or require 230V.
 

Reply to Looking for an easy-to-understand explanation of 3 phase / 3 phase + N in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
334
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
23
Views
1K
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K
I didn't get a picture so will have to wait until I go back again but I've done a crude drawing of what was there. Its in a commercial set up...
Replies
13
Views
2K
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top