So today, I get a phone call from one of the bosses customers. No power or lights in workshop. (3 phase DB feeds single phase DB).

Says the lights flicker on when 3 phase compressor tries to run. My guess over phone was a lost phase, or neutral problem

The boss went out later and confirmed my thoughts. One of the main fuses had blown.

Can any of you more intelligent people explain the flickering lights?
 
As Telectrix said, most likely the motor acted as a generator when running with 2 of the 3 phases. Not going to end well for the motor mind...
 
A running 3-phase motor that loses one line will attempt to regenerate the missing phase and supply any connected loads. Its torque will be severely reduced and the current in the remaning two lines will shoot up, so it is likely to trip or stall very quickly. However, on a motor running mechanically light with minimal load on the missing phase, the singlephasing condition might continue for some time unless the overload relay is designed to detect it.

However, a 3-phase motor will not generally start from a standstill with one line missing even when lightly loaded. The remaining two lines only make one phase out of the three, so there is no rotating component of stator flux to give it an impetus in one direction or the other, just like a single-phase motor with its start winding or capacitor winding disconnected. However, it will still act like a (bad) transformer and deliver some voltage into the missing line. If the load is heavy enough, i.e. there is a low enough resistance to neutral, it will function as an assymmetric 3rd phase and generate some torque, which might be enough to spin-up a very light load, but by then one would hope the O/L will intervene.
 
Last edited:

Reply to Lost a phase. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Recently started a retrofit where the 3 phase dB has been fitted with bushes through the galv trunking. The single phase supplies outgoing have...
Replies
1
Views
272
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
686
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
1K
Hi all, any advice would be greatly appreciated. Went to do some work at a factory unit on Monday ( changed 20 florries to LED battens and changed...
Replies
3
Views
637
What can be worse than electrical installations on a farm, or in a pub?...... Chippys! Got a phone call from my local.... Lights and kitchen...
Replies
6
Views
852

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock