Discuss Low Insulation resistance test on smoke detectors in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

King84

Trainee
Reaction score
14
Hi Everyone

Just a question bothering me as you cannot do Insulation resistance test on smoke detectors as they can become damaged so obviously smoke detectors are sensitive but they are also installed on lighting circuit so if perform low insulation resistance test 250V between Live and earth would that be safe or still they should be disconnected first or if not possible then it is a limitation ?
 
SOme of these are badly fitted and I sometime avoid taking them down incase if they dont fit back properly so was wondering if I could test with low IR by using Line,Neture together with earth
 
You can test at 250VDC but the internal circuitry of the heads will probably give you poor readings.

Best to do line/neutral to earth, I tend to do 250VDC first in case of current using equipment still fitted that might throw your results such as switched mode power supplies, the 500VDC if I'm happy to proceed.

I'm guessing this is for periodic inspection rather than new installation?
 
SOme of these are badly fitted and I sometime avoid taking them down incase if they dont fit back properly so was wondering if I could test with low IR by using Line,Neture together with earth

If they’re badly fitted I’d still want to take them down before testing, then code accordingly and rectify where needed.
 

Reply to Low Insulation resistance test on smoke detectors in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
588
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
I have installed a circuit for an oven and carried out all of the relevant testing so far. Apart from a neon on the double pole isolation switch...
Replies
9
Views
2K
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
758
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
709

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock