Discuss Low IR test readings on lighting and RFC. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
4
Hi,guys went to do an EICR and when doing IR test I got L-E ON RFC like 0.02 MOHM and two lighting circuits L-E AND L-N the results were like 0,14 and 0,15 MOHM.It is old wiring where all the cables live and neutrals are black put in the walls in steel conduit.My question is is it possible that low readings are due to dumpness in the wall?Took one light down and can see dumpness on the cables.Doe to time limit coulf not disconnect everything,but surely L-E and N-E should give some higher readings.Thank uou in advance for all help.
 
Check if there are any RCD sockets/FCU on the circuit.

I have been caught before discovering they have a low-ish internal resistance to the CPC (presumably to trip if wiring fault?) and after disconnecting them it went to the ~10M or so I would prefer to see.
 
It is what it is. I will have a quick scan as per @pc1966 looking for obvious causes but aside from that record the figure you get. Forget L to N readings on an EICR.
 
Filtered sockets or extension blocks always cause low IR readings on RFC's
Damp will obviously cause problems with IR but more likely at a termination than the actual cable (unless cable is damaged of course).
 
Filtered sockets or extension blocks always cause low IR readings on RFC's
This is another good point. If you ever see low IR then re-test at 250V, if you get a really big difference (going from < 1M to > 10M sort of thing) then it has all the hallmarks of an SPD in some multi-way block or similar.
 

Reply to Low IR test readings on lighting and RFC. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
671
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
696
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
767
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
504
Recently changed a CU for a friend and today when visiting one of the RFC's RCBOs tripped. It was due attention anyway as open ring and no time to...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock