Discuss Low Ze, high PFC in industrial application in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
6
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC 5.75 kA.

Obviously this is a three phase supply, so shouldn't they have doubled the PFC and reported it as 11.5 kA, or is this business of doubling the phase fault current to estimate the short circuit current between all phases a recent thing?

The second problem - is there a reliable means of measuring such low Zes, or is it a fool's errand and you're best just calculating it? From a number of different tests, I'm gaining the impression that the real impedance might be nearer 0.03 R - a small difference, but that would make IPF 50% larger (230/0.03 = 7,666.7 x 2 = 15.3 kA). Even with all best practice my Fluke 1664 reads anything from 0 R to 0.03 R. Note that it's never given a higher reading, which is partly why I think the Ze on the EIC is suspect.

The third problem - I bet you know what I'm about to say! - there're a couple of 400v distribution boards full of 3 pole MCBs with 10kA breaking capacities. Zdb won't be meaningfully greater than Ze at the origin, one is fed off the bus bars, the other from a short run 16mm2 cable (Zdb is still so low I'm struggling to measure it - 0.02 R is commonly returned). Unless I've got something wrong or misunderstood something, the breaking capacity is inadequate - or was is OK to rate them on the single phase fault current 20 years ago? Even if the Ze on the EIC is correct, 2 x 5.75 kA = 11.5 kA.

Thanks.
 
It is possible for the supplier fuses to solve the problem in some circumstances, as the PFC can cause a supplier fuse to blow before the fault current reaches the 10kA breaking capacity of the breakers.
So to be sure, more info about the supplier fuses would be needed. If it's an 100 amp supply or less, at first glance it seems that the fuses would interrupt proceedings at 5 kA if you had 15kA PFC.
 
It is possible for the supplier fuses to solve the problem in some circumstances, as the PFC can cause a supplier fuse to blow before the fault current reaches the 10kA breaking capacity of the breakers.
So to be sure, more info about the supplier fuses would be needed. If it's an 100 amp supply or less, at first glance it seems that the fuses would interrupt proceedings at 5 kA if you had 15kA PFC.
Thanks, I wondered about that. From a purely electrical point of view then, if any fuses upstream of the 400V distribution boards had sufficient breaking capacity AND would blow faster than the MCBs' disconnection time at PFC, we'd be home and dry?

It's just that the regs don't make any mention of what's upstream of the DB. As far as I can make out, the letter of the law is that the MCBs should be rated for the PFC at that point?
 
It's just that the regs don't make any mention of what's upstream of the DB. As far as I can make out, the letter of the law is that the MCBs should be rated for the PFC at that point?
I think 434.5.1 , 2nd paragraph, is the bit you are searching for.
I'm not saying it isn't a problem, just that it might not be a problem depending on what rating fuses are where.
 
Having fuses or MCCB up-stream of the MCB can result in a safe situation, but you really ought to check with the manufacturer for the cascaded breaking capacity. Some are good at supplying this (e.g. the Hager commercial catalogue has tables near the back, Schneider has an on-line tool to compute selectivity and break limits, etc) but others are rubbish at real technical support.

In some cases you can take fuse graphs and plug in your estimated values to get some idea. This was one I posted here a bit back about domestic CU and how the typical 6kA MCB are safe (by design/certification) to 16kA PFC as a result:
BS88-fuse-with-MCB.jpg


Of course the details can be more complicated than simply looking at peak current limit of the fuse versus symmetric PFC equivalent, etc, but it shows the basic idea.
 
Obviously this is a three phase supply, so shouldn't they have doubled the PFC and reported it as 11.5 kA, or is this business of doubling the phase fault current to estimate the short circuit current between all phases a recent thing?
It depends on how you measure it, and to some extend the nature of the supply (i.e. how impedances limiting the current arise).

If you have a typical measured single-phase L-N or L-E PFC value then you are seeing the result of U/(R1+Rn) or U/(R1+R2)

If you then have a "bolted three phase fault" you are seeing no impedance on the "virtual neutral" line as all three L currents sum to zero at the fault, so the limit is now U/R1

Assuming R1=Rn then that is double the L-N PSCC value, hence that approach. But if Rn is not comparable for whatever reason, it is not such an accurate measurement.

Another approach is you measure the L-L PSCC values instead, in this case to get the worst-case "three phase bolted" fault current you multiply L-L values by 2/sqrt(3) = 1.15 This approach has the advantage of not including Rn or R2, so it is more accurate, assuming your tester is safe & able to do the PSCC measurement on a nominal 400V supply.
 
For doing big stuff you can get special high current loop impedance testers.

I have never used one but the DNO style folks have access. Basically it has both a bigger on/off test current to get more delta-V to measure, and uses 4-lead "Kelvin" clamps to measure the impedance on the terminals without crude corrections for the test cables and their contact impedance.
 
It depends on how you measure it, and to some extend the nature of the supply (i.e. how impedances limiting the current arise).

If you have a typical measured single-phase L-N or L-E PFC value then you are seeing the result of U/(R1+Rn) or U/(R1+R2)

If you then have a "bolted three phase fault" you are seeing no impedance on the "virtual neutral" line as all three L currents sum to zero at the fault, so the limit is now U/R1

Assuming R1=Rn then that is double the L-N PSCC value, hence that approach. But if Rn is not comparable for whatever reason, it is not such an accurate measurement.

Another approach is you measure the L-L PSCC values instead, in this case to get the worst-case "three phase bolted" fault current you multiply L-L values by 2/sqrt(3) = 1.15 This approach has the advantage of not including Rn or R2, so it is more accurate, assuming your tester is safe & able to do the PSCC measurement on a nominal 400V supply.
Many thanks for that. Most modern testers with the high current two wire test allow one to measure phase to phase Ipf so I'd argue that's probably the best way.

In this particular application it's a TN-C-S and there's no measurable difference between the phase-neutral and phase-earth impedances (although as I mentioned earlier, the instrument gives different readings every time I do the test at this very low Ze!).

On the specific point of what was written on the original EIC though, I presume was technically incorrect to record the single phase PFC? It's certainly not what I was taught or in line with what it says in GN3 etc.
 
Many thanks for that. Most modern testers with the high current two wire test allow one to measure phase to phase Ipf so I'd argue that's probably the best way.

In this particular application it's a TN-C-S and there's no measurable difference between the phase-neutral and phase-earth impedances (although as I mentioned earlier, the instrument gives different readings every time I do the test at this very low Ze!).
Really anything below about 0.1 ohm is not that accurate on your typical MFT. The better ones give an accuracy specification but it is not that good at low impedances, largely as the test leads and contact resistance can vary by 0.01 ohm quite easily.

On the specific point of what was written on the original EIC though, I presume was technically incorrect to record the single phase PFC? It's certainly not what I was taught or in line with what it says in GN3 etc.
There are two things:
  • The PFC is L-E and that is "as measured" for the Zs/Ze value with the view to deciding if supply fuse/MCCB can meet ADS on an earth-fault, and to allow computation of down-stream Zs by adding R1+R2
  • The PSCC is worst-case fault to decide if breaking capacity is sufficient. That would be typically be double the max measured L-N value for the 3P case. L-E can be higher in some cases (TN-S with many parallel earth paths, for example) but rarely that much higher to be considered.
 

Reply to Low Ze, high PFC in industrial application in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
So Ze=0.02 and R1+R2 = 0.73 on a first floor ring main. Nearest submain is about 35m away, so that Ze's plausible, and even a slightly indirect...
Replies
61
Views
6K
Hi Guys, Have just done a DB change in a Barbers in a high street. Carried out a Ze and my Megger shows less than 0.01 ohms...!!! Instantly...
Replies
15
Views
4K
S
I have a three phase dis/board with a measured PFC of 10 kA across each phase (20 kA total) and a Ze of 0.03. The origin is 100 amp BS 1361 type...
Replies
4
Views
3K
Engineer54
E
V
Hey guys, i have started to do some inspecting and testing, i am finding it very interesting although the certification part is a little confusing...
Replies
26
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock