520
carrying out an eicr on a building recently we found the external ze reading to be extremely low ie 0.02ohms. so by measurement and testing are fault current read 20ka. now most of the mcbs rcbos ets have an icn of 10kohms. this poses a problem as obvisoluy the mcbs etc would self destruct under fault conditions. what would you code this and more importantly how would we rectify this problem, Interested to here your thoughts.
 
2 options available,

1 extend the supply cable by running a length of swa from incomer to fuseboard, 50m would probably bring the reading down enough.

2 change the breakers to a higher rating of fault current.
 
I had a case where I was measuring about 3m away from transformer and the meter was giving readings that were far higher than I expected.
changed the values on cert. to what the transformer manufacturer stated.
 
are you suggesting I cheat and higher the ze reading. ha ha
not cheat,
figure can be found by measurement or investigation.

if the transformer manufacturer says max pfc is 20Ka and the meter reads 92Ka then the manufacturer wins on my paperwork.

all the meters suggest that they may be inaccurate when close to transformer but not 1 of them says in the instructions that below x meters away you should ignore the reading on meter!!
 

Reply to LOW ZE READINGS in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
1K
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
47
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock