Discuss Mains RCD tripping on larger MCB's in the UK Electrical Forum area at ElectriciansForums.net

Your relative should be able to open the consumer unit,disconnect all the circuit neutrals,check the resetting of the Rcd
If it now resets,the neutral conductors can be replaced one at a time to see if balance is maintained
If he is an electrician (of whatever discipline)and have test meters,the problem should be easy to identify
 
Your relative should be able to open the consumer unit,disconnect all the circuit neutrals,check the resetting of the Rcd
If it now resets,the neutral conductors can be replaced one at a time to see if balance is maintained
If he is an electrician (of whatever discipline)and have test meters,the problem should be easy to identify
Brilliant, thank you very much :)
 
Really appreciate the response I've received from this, great group.
I'll try the advise given to see if we can individually identify something.
My relative is a electrician but unfortunately in the industrial trade.
I reckon they would be willing to have a look at it for me, is there any type of tester I could advise them bring along with them.
Failing that, looks like I will be contacting a local sparky as mentioned I've noticed the RCD not easy to get a like for like now.
Thank you
If the relative you speak of is an Electrician, he/she must be able to sort this fault out for you, after all he.she is an Electrician
 

Reply to Mains RCD tripping on larger MCB's in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I'm after advice on how best and safely to do a friends Fuseboard upgrade. Current setup is a Wylex 6 Way board with MCBs of 2x 6A, 2x 32A and 30A...
Replies
2
Views
178
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
816
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
905
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock