Discuss Max Zs measurement allowed in the UK Electrical Forum area at ElectriciansForums.net

Here’s a pic from the lighting CP
 

Attachments

  • IMG_6220.jpeg
    413.2 KB · Views: 30
The breakers shown in the (blurry) picture seem to be these - ABB 60898 S271 type C, not BS3871 type 3.
There are datasheets for these that include the time/current charts.
I don't know if this helps at all...
If they are usual type C (instant trip point = 5-10 * In) then you can calculate Zs for cold testing (assuming ~70C operating, etc) as:

Zs = 80% * Umin / Imax = 0.8 * (230 * 0.95) / (13 * 10) = 1.34 ohms
 

Reply to Max Zs measurement allowed in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Still having a discussion @ work about this…TNCS system DB/CU is a split 30ma RCD configuration,5/5 MCB’S are 60898 what Max Zs would you put in...
Replies
31
Views
1K
Hi everyone, Happy Friday! Could someone please point me in the right direction, I’m after the Max Zs for a Bill Talisman TLF633 63A MCCB, I’ve...
Replies
4
Views
1K
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
482
hello , can anyone reccomend a free download for max zs values for bs 3871 ct breakers please
Replies
2
Views
1K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock