Discuss max zs of large fuses in the Commercial Electrical Advice area at ElectriciansForums.net

P

peterhardacher

BS7671 tables only go to certain size fuses eg how can I find max ZS of 400 amp BS88 - 2 on niceic test sheets they ask for a max value out of regs table I have only managed to find a busman fuse chart which differs been told by employer to use these values on sheets any input would help thanks
 
ThAnks struggling to get such information though that's what I been using but only got busman available and don t get any time to search for such info the boss gave me this info
 
Bussmann gG fuses to BS 88: Parts 2 and 6 are:
Rating (A) Zs (Ohms) Rating (A) Zs (Ohms) Rating (A) Zs (Ohms)
6 14 50 1.1 250 0.16
10 7.7 63 0.86 315 0.13
16 4.3 80 0.60 400 0.096
20 3.0 100 0.44 500 0.073
25 2.4 125 0.35 630 0.054
32 1.9 160 0.27 800 0.0

MEM state 400amp BS88 part 2 & 6 is 0.094 so they are about the same m8
 
BS7671 tables only go to certain size fuses eg how can I find max ZS of 400 amp BS88 - 2 on niceic test sheets they ask for a max value out of regs table I have only managed to find a busman fuse chart which differs been told by employer to use these values on sheets any input would help thanks

Mores the point, do you have test equipment that can test to those low values?? Which brings us back to another threads discussion, on the need for HR test equipment!! lol!!
 
I love this subject, it’s so woolly.

I’ve had heavy faults where the fuse has survived and the upstream protection has gone first. Others where the fault let through was to great for the fuse and its not contained the fault.
I had nothing to do with the design of the systems, I inherited them “as is” and was stuck with them.

Never had a 1600A fuse blow and I’m glad of that. The 11KV protection picked it up first every time. The biggest fuse I’ve dealt with was 3200A.
 
Thanks for the reply very helpfull and no my meters provided cannot read such low values I was discussing this with one of the lads the other day that normal meters are not acurate below 0.01 ohms I think this is correct and to be honest this was the first I had heard of this ( hopefully not sounding stupid. ) I have been provided with niceic sheets not very industrial friendly in my opinion . Thank god for smart phones eh what a handy app this is when ya need to ask some advice as the boss will tell ya anything to get them sheets. Signed lol :)
 

Reply to max zs of large fuses in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi All, Can anyone help with calculating a Zs value for the fuse described in the title. The fuse sizes in Fig 3A3(c) of the 18th edition wiring...
Replies
1
Views
968
I am helping a local football club who are having some issues with Zs being too high on the submain. They have the supply Henley blocked into a...
Replies
9
Views
2K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi all, Just wondering if anyone can shed some light on the max zs values in the OSG, they don’t seem to follow the 1.25 divisor stated in the...
Replies
10
Views
7K
Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Replies
32
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock