Hi All,
Thank you for welcoming to this forums

I just want to clarify that the Value I need to enter 100% or 80% in the last column "Maximum Zs Permitted by BS7671"
is it 80% from the table 41.3 from 18th Edition Regs - Page 62 or the value from Pocket Guide 18

Thank you
Loges
 

Attachments

  • Pocket-Guide-18.pdf
    801 KB · Views: 51
As Strima says, you put down the value found in BS7671.
This is so the customer gets confused when the measured value is less but it still fails.
but then you confuse them even more by telling them it's oK, with RCD it's 1667.
 
BUT 80% is not max. it's corrected assuming cable will be fully loaded and at 70 deg.C. this will never happen. cables will be at least 30% overloaded and breaker will trip long before that temp. is reached (assuming circuit has been designed in compliance with 7671). tin hat on.
 
BUT 80% is not max. it's corrected assuming cable will be fully loaded and at 70 deg.C. this will never happen. cables will be at least 30% overloaded and breaker will trip long before that temp. is reached (assuming circuit has been designed in compliance with 7671). tin hat on.
Absolutely agree. I don’t understand why we even use 80%. It is overkill.
I think 90-95% would be adequate just to allow for design flaws and anomalies.

However the Cmin factor that gives 95%. So I recon that should be sufficient.

Obviously there may be very good reasons 80% is used. Maybe a figure plucked out of the air. I don’t know. Any ideas?
 
BUT 80% is not max. it's corrected assuming cable will be fully loaded and at 70 deg.C. this will never happen. cables will be at least 30% overloaded and breaker will trip long before that temp. is reached (assuming circuit has been designed in compliance with 7671). tin hat on.

The maximum ALLOWED value of Zs is the 100% value
The maximum PERMITTED value of Zs is the 80% value

Pretty clear cut IMO and provides a reasonable margin of error for any changes in the environmental or installation conditions

I would rather work to the 80% value than be trying to talk my way out of a stay at one of Her Majesties hotels because I used the 100% value and it all went wrong
 
I would rather work to the 80% value than be trying to talk my way out of a stay at one of Her Majesties hotels because I used the 100% value and it all went wrong
It wouldnt go wrong with the 100% value, the difference in disconnection time would be marginal or non-existant in real, not calcualted situations. Nobody will ever be prosecuted for using the maximum value of Zs clearly written in the regulations.
 
It wouldnt go wrong with the 100% value, the difference in disconnection time would be marginal or non-existant in real, not calcualted situations. Nobody will ever be prosecuted for using the maximum value of Zs clearly written in the regulations.

You really missed the point
If the installation following an incident was found to exceed the maximum allowed value then you would probably end up explaining to a person wearing a funny wig why
 
The EIC has a note for permitted values.
Where the maximum permitted earth fault loop impedance value stated in column 8 is taken from a source other than the tabulated values given in Chapter 41 of this Standard, state the source of the data in the appropriate cell for the circuit in the ‘Remarks’ column (column 25) of the schedule.

That note indicates you are expected to use the values from the various tables in Chapter 41.
 
The EIC has a note for permitted values.
Where the maximum permitted earth fault loop impedance value stated in column 8 is taken from a source other than the tabulated values given in Chapter 41 of this Standard, state the source of the data in the appropriate cell for the circuit in the ‘Remarks’ column (column 25) of the schedule.

That note indicates you are expected to use the values from the various tables in Chapter 41.
I think the OP is referring to standard protective devices in BS7671.
 
The test sheet asks for the maximum permitted value of Zs which is clearly the 80% value
No it’s not as the conductors are not at full load current or indeed at any current for initial verification and do bare in mind that we have to adjust the temperature again if called for.
 
The EIC has a note for permitted values.
Where the maximum permitted earth fault loop impedance value stated in column 8 is taken from a source other than the tabulated values given in Chapter 41 of this Standard, state the source of the data in the appropriate cell for the circuit in the ‘Remarks’ column (column 25) of the schedule.

That note indicates you are expected to use the values from the various tables in Chapter 41.
Is that not for using the manufacturers data/Zs values for their ocpd rather than the generic values of bs7671?
 
The EIC has a note for permitted values.
Where the maximum permitted earth fault loop impedance value stated in column 8 is taken from a source other than the tabulated values given in Chapter 41 of this Standard, state the source of the data in the appropriate cell for the circuit in the ‘Remarks’ column (column 25) of the schedule.

That note indicates you are expected to use the values from the various tables in Chapter 41.

this is what i was told on my 2391 course.

but it makes no sense to me as GN3 makes a big deal about correcting for temperature and then the IET forms appear to indicate that the cold measured value should be compared directly to the hot values from BS7671.
 
You really missed the point
If the installation following an incident was found to exceed the maximum allowed value then you would probably end up explaining to a person wearing a funny wig why
I don't miss the point at all, it is extremely unlikely that a value at or below the 100% mark but above the 80% would have any bearing whatsoever on an 'incident' sufficiently serious to go to court.
And given the almost universal use of RCD protection for final circuits now in many installations it's really a moot point as the permitted max Zs is likely to be 1667 ohms. Suddenly getting silly over a fraction of an ohm seems a bit superfluous.
 
esp. as bs7671 gives same values of PFC for both 0.4 secs and 5 secs. that can't be right.
 
Is that not for using the manufacturers data/Zs values for their ocpd rather than the generic values of bs7671?
Not sure what you mean?
The note is telling us that if we don’t use the values from the tables in chapter 41, then we need to record where we are getting the values from in the box for remarks.

So yes, if you are using values supplied by the manufacturer, make a note.
Also if you are recording the 80% value rather than the value required from the tables in chapter 41, make a note.

At the end of the day, the only use of these forms, is as a comparison with the form produced at the next inspection.
 

Reply to Max Zs Permitted by BS7671 value in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Does anyone know where I can find the maximum Zs values for AFDD's? Table 41.3 refers to 60898 and 61009-1 but AFDD's are BS 62606
Replies
4
Views
5K
Got my am2 coming up on Tuesday and I know I have to calculate my Zs readings Maybe I’m overthinking this but am not sure if I need to use the Ze...
Replies
17
Views
3K
I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Replies
4
Views
2K
Hi all, I have an assessment exam question that asks for the design value for a 32A 60898 MCB max Zs. By 'design' value is this the regs tabulated...
Replies
7
Views
2K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock