Discuss Max zs values in the Electrical Engineering Chat area at ElectriciansForums.net

Yep but what 5 second requirement I can't see one except 5 sec is for distribution circuits of & above 32amp ?
Those are your cases for a 5s disconnect time, subject to thermal limits on the cable (e.g. adiabatic check).

Normally you would always aim for 0.4s or below even if not explicitly required, but there are cases when you look at the 5s limit. For example:
  • For high current sub-main or fixed circuits you may not be able to meet 0.4s due to Ze anyway
  • On a sub-main you might push the upstream OCPD as high as the 5s or adiabatic thermal limits allow to get better selectivity with the down-stream DB MCBs.
[automerge]1590238260[/automerge]
yeah both aren't really needed if you just do the simple equation.
Except when the simple equations is very wrong. Yes, if you know it is a B-curve MCB, but in other cases you can get it wrong by a factor of 2 or so.
 
Those are your cases for a 5s disconnect time, subject to thermal limits on the cable (e.g. adiabatic check).
The OSG book in Appendix B has tables that include the typical adiabatic limit for the common CPC sizes so it is your easiest option for selecting an OCPD when desiging something like a garage CU feed, or verifying an existing OCPD and measured Zs is reasonable.
 

Reply to Max zs values in the Electrical Engineering Chat area at ElectriciansForums.net

Similar Threads

Hi All, We have a Merlin Gerin Compact NS100N Single Phase MCCB I've been asked to find its Max ZS Values and to be honest I cant find anything...
Replies
6
Views
3K
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
2K
Now Ive done Periodic Inspection and Initial Virification Qualifications with LCL/EAL (so non C&G 2394/95) # strange part building Modules , this...
Replies
6
Views
981
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi all, I have an assessment exam question that asks for the design value for a 32A 60898 MCB max Zs. By 'design' value is this the regs tabulated...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock