Discuss Maximum Cable Length! in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

V

videz6

can someone please help me with this question

There is a 40A BS88 fuse, protecting a 10mm cable with a 4mm Earth, it is wired to Reference method C, supply is TNS and it is protected by a 30mA RCD. What is the maximum length the cable can be?

(thats all the info i have! I haven't been to collage for couple of years now and cant remember how to do it )
 
find max zs then deduct ze wich will leave r1+r2 rearange formula to make length the subject:

r=mva x length/1000

so

l=r x 1000/ mva

that should work
 
Ring circuit

4 x (Max Zs - Ze) ÷ ((R"1 + R"2) x Cr)


Radial

(Max Zs - Ze) ÷ ((R"1 + R"2) x Cr)


R"1 + R"2 = Resistance per meter of Line & Cpc conductors
Cr = Correction factor for conductor operating temp of 70°C

So lets assume your Ze is 0.8 (max for TN-S). The max Zs for a 40A BS88 fuse is 1.35Ω and the R"1 + R"2 of 10/4.0mm² cable is 6.44mΩ per meter.

The calculation would be:

(1.35 - 0.8) ÷ ((6.44/1000) * 1.2) = 71m

However most maximum circuit lengths are limited by Voltage Drop and the voltage drop of 71m of 10mm² cable carrying 40A is 12.5V which exceeds the 11.5V (5%) maximum VD for a power circuit.

VD = mV/A/m x Length x Current
VD = (4.4/1000) x 71 x 40 = 12.5V


So you would need to work out the max length for Voltage Drop

Ring

4 x (Max VD x 1000) ÷ (mV/A/m x Current)


Radial

(Max VD x 1000) ÷ (mV/A/m x Current)


So for your circuit the calculation for VD would be

(11.5 x 1000) ÷ (4.4 x 40) = 65m
 
Last edited by a moderator:

Reply to Maximum Cable Length! in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

This question has probably been asked several time but things change. The house I'm living in now was built in the 1960's and has a ring main...
Replies
15
Views
936
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
668
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
527
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock