Discuss Maximum demand in the Australia area at ElectriciansForums.net

B

blenki

Hi , when filling in the Maximum demand on the EIC do you guys work out everything based on diversity or do you add up all the MCB's then multiply by 0.66. I keep hearing different versions ,some people just put down the cut out fuse value
 
The maximum demand will usually only be the fuse value as it cat pull anymore than that!

To be honest, i dont think there is a strict requirement to be spot on.

I know some sparks put down the biggest MCB size.
 
Hi Blenki
What i do is turn everything off in the house and use a clamp meter on meter-cu line and turn everything on in the kitchen (cooker/hob/toaster/mike/lights/all sockets plug in something and switch on ) this should give you the total load of the property.
Regards
Kung.
norm find its about 54amps for a 3 bed house.
 
Last edited by a moderator:
Thanks lads , ive got part p assessment coming up and i want to make sure i can answer him if he asks , il probably work out all the diversitys of each circuit then add them up. just wondered if you lads who have been in the trade a while have a quicker way of doing it
 
problem i got is with 2x32a ring circuits (100% of first ring then 40% of second)
1x32a boiler circuit (assuming 100% diversity)
1x32a cooker circuit (cooker rated at 30a before diversity)
2x6a light circuits (around 8x 100w lamps on each circuit)


I GET JUST OVER 100A IF IM DOING IT RIGHT
 
problem i got is with 2x32a ring circuits (100% of first ring then 40% of second)
1x32a boiler circuit (assuming 100% diversity)
1x32a cooker circuit (cooker rated at 30a before diversity)
2x6a light circuits (around 8x 100w lamps on each circuit)


I GET JUST OVER 100A IF IM DOING IT RIGHT

If the boiler circuit is only doing a boiler,pump,controls could that be reduced to 16a or less.
 
I was under the impression that you should take account of diversity when working out maximum demand.(tin hat on). If you apply diversity to the cooker and 2nd ring your total is still less than 80A even if there is a socket on the cooker point.
 
Hi Blenki
cooker is first 10A then 30% of the rest of it (plus 5A if there is a socket outlet on the cookerpoint). Lighting is 66% of max. Ring is 100% of first one and 40% of second.

you said cooker was 30A so that is 10A plus 30% of 20 = 16A ( or 21A if there is a socket outlet)
first ring 100% = 32A
2nd ring is 40% of 32A = 12.8A
Lighting 800w/230V=3.5A x2=7A X 0.66% = 5A

total demand = 66A ( or 71A if there is a socket outlet on cooker)

(rounded figures up)
 
hi pushrod thats the way i worked it out , but you have missed out the boiler circuit (i allowed for 32a worst case scenario ) as i dont know what the boiler is taking. i cant see it taking 32a so it should be under 100a max demand. Thanks for the reply
 
sorry didn't notice the boiler - what type is it ? I assume it is not a gas boiler as the current demand to that is tiny. If it is an immersion heater it is probs 3 KW with an approx 13A demand. It would probably be worth looking at it and seeing if you can find a power rating on it. Allowing 32A for it would mean that it was a 7kW+ heater (very unlikely unless it was a shower) You are right that there is no diversity allowed on a water heater.
 
cheers pushrod , got my part p coming up so i want to make sure i get it right . as long as the max demand comes under 100a il be happy:D
 
Hi , when filling in the Maximum demand on the EIC do you guys work out everything based on diversity or do you add up all the MCB's then multiply by 0.66. I keep hearing different versions ,some people just put down the cut out fuse value


hi there

i take it that you are the designer of the installation yes / no ?

Maximum demand is considered at the design stage and as such you should have to hand all the designers calculations for each circuit to be installed to ensure that you meet BS7671 :rolleyes:

If you are installing and testing etc if you stick to all the books then ok you will meet maximum demand etc. :)
It is really down to what you have installed at the time and in the design any future use which may take in expansion etc. :confused:

looking at each circuit in a common sense way ie lighting will the put a cooker on it ?:D
ie 32 amp ring final circuit its cold the heating's packed up outcome 15 3 k watt heaters etc.:eek:

i think you look at the whole of the installation and make a calculated common sense judgment on what you have and what you may be likely to expect in service use

there is a design guide by the iee electrical installation design guide isbn 978-0-86341-550-0 which give more details etc of maximum demand etc mainly aimed at designers

cheers alll
 
Last edited by a moderator:

Reply to Maximum demand in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
Bit of a rant first to explain the situation:- Effing builders again, I knew there was a reason we hardly ever work for them. We've done a few...
Replies
12
Views
584
I'm always in a dilemma with regards max demand. Often you work it out and it's higher than the the 80A or 60A cut out fuse. However, you know...
Replies
5
Views
2K
So I just started out recently and I’m struggling with what to price myself at. It’s worth noting I live in the east London area and I’m looking...
Replies
12
Views
601
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
637

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock