Hello,
Could any Irish members on here either tell me the maximum number of lighting points permissable on a circuit?
I seem to remember a FĂ s teacher mine saying that it was 10. The reason being that it's to do with a property being put into darkness in the event of a fault. I also think that he showed us the page in the ETCI book.
I've looked in the ETCI book and I've failed to find anything regarding the above.
If amyone could help with the above that would be great!

Thanks
Farmer
 
The maximum recommended number of points for a radial circuit is given as ten. This is in an Informative Appendix. Therefore, contrary to popular belief, this is suggested good practice and not actually a Rule.
 
OK, @farmer as promised you will find it in Annex 55A (Final Circuit Arrangements.)

As mentioned this is an Informative Annex and therefore does not form part of the Rules but could be seen as good practice which generally it might be better to observe.

If you go to 4.2 in Annex 55A you will find "Radial final circuits for socket-outlets and appliances in domestic and similar installations".

This gives a "recommended maximum number of points: 10 (see the definition of "point"). One point may serve a single or double socket-outlet."

In 4.1 are "Radial final circuits for lighting equipment in domestic and similar installations".

This states that "at least two radial lighting circuits should be provided for a normal dwelling or similarly sized premises."

Hope this helps clarify this for you.
 

Reply to Maximum number of lighting points in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
Replies
63
Views
5K
So I am a fully qualified spark with my own company, however I also have a few properties I rent out. One of my tenants asked if they can have an...
Replies
84
Views
11K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
47
Views
8K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock