Discuss Maximum ZS exceeded on RCBO in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

newfutile

-
Esteemed
Arms
Supporter
Reaction score
388
On a recent EICR i have ring final circuits (sockets) on type C 32 amp rcbo
Some of my ZS reading exceed maximum ZS (0.55 OSG) ie:0.65 ohms .

On a earth fault this will disconnect via the MCB part of the RCBO.
How can i ensure a LINE to Neutral fault will still disconnect?
 
Was the Zs measured or calculated?

Was it tested using a no trip setting?

Any dead test results (R1+R2)?

What's the Ze?

PFC?

Did you do a Zn measurement?
 
What protective purpose is the RCBO serving?
 
Was it tested using the no trip setting on the meter?
 
As one or 2 others have inferred, you have probably adhered to the regulations and fault protection simply by using an RCBO. If you use the RCBO for fault protection then you only need a Zs value <1667ohms. This is acceptable as per reg 411.4.5. However, I can't quite get my head around being able to just use the RCD and ignore the max Zs figures on a TNS or TNCS.
 
On a recent EICR i have ring final circuits (sockets) on type C 32 amp rcbo
Some of my ZS reading exceed maximum ZS (0.55 OSG) ie:0.65 ohms .
As other have pointed out, the RCD aspect will disconnect (if it is working) for a wide range of Zs value.

Normally I do not advise relying on a single RCD for disconnection, however, here you are only a little above the OSG Zs limits and when you consider they take the upper MCB trip point, the lowest (almost) mains voltage, and allow 20% for heated conductors, you see there is a lot of margin built in.

So in your place with just the single RCD function of the RCBO guaranteeing ADS I would not worry, as the OCPD aspect will probably meet it (and certainly would if you have a couple of seconds for the thermal trip to go).

While the typical 30mA RCBO is theoretically compliant to 1.67k Zs (from 50V/30mA) the only excuse for anything other than a couple of ohm Zs is Ze being high due to a TT earth rod, and then it should not exceed 200 ohms (from regs 411.5.3 'NOTE 2' below Table 41.5)
On a earth fault this will disconnect via the MCB part of the RCBO.
How can i ensure a LINE to Neutral fault will still disconnect?
Usually if you do a Zs measurement at the end of a circuit you normally get both the PFC and the PSSC from most MFT. If the PSSC is high enough then your L-N loop is fine for disconnection. In the general C-curve MCB that is 10 times the rated In value, though you should make some allowances for low volts and heated conductors.

If your PSSC is 20 times the rated current (load current for fixed fixed loads, the MCB 'In' rating for general/socket systems) then you have also verified the 5% volt drop requirements.

As a general rule, if the PSSC is significantly less than the PFC you should check. If that is due to metal trunking, conduit, and other parallel earth paths, then fair enough. But if no explanation is found then it is a reason to check the Rn as well as R1 values independently.
 
Last edited:
If your PSSC is 20 times the rated current (load current for fixed fixed loads, the MCB 'In' rating for general/socket systems) then you have also verified the 5% volt drop requirements.
Just to add, the "20 times" test is verifying the total supply VD, not just the final circuit, so it is more demanding than often used for design.

For final circuits that are a small fraction of the DB supply rating it is more or less the same. But for circuits that are a significant portion of the DB then you might not need to meet 20x as somewhere there would be an allowance for the supply VD, and separately for the circuit VD.
 

Reply to Maximum ZS exceeded on RCBO in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Replies
4
Views
2K
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
2K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock