Discuss Maximum Zs values and the rule of thumb in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

G

gareth020

Hello, can someone explain to me the 'rule of thumb figure' (0.8) when calculating max Zs value's from BS7671!?
Currently doing a PIR in a foundry where i measured the ambient temperature at 21 degrees at ground level, i bet you can add another 10 degree's higher up ...and that's on a good day. Anyway surely i don't need this 0.8 rule in this situation and i'll use the values given in the regs!??? Or should i be calculating the values myself!???

Thank You
Gaz
 
Last edited by a moderator:
on your cert. you enter the value given in brb. you hope to achieve a ZS value of below the 80% temp. corrected figure. e.g. 32AQ type B is 1.44 in brb. 1.15 corrected. the lower the measured value, the better.
 
Zs values in the BRB are take at an operating temp of 70 C.

When your testing the circuit wont be at 70 C Obviously.

Copper has a coefficient of .004 per 1 degree.

So if your conductor is the same temp as your ambient lets say 20 C, we need to make an allowance for testing.

So 70 C - 20 C = 50 C so 50 x .004 = .2

If we take the Zs values as a factor of 1, then 1 - 0.2 = .8

So 32 amp type B mcm Zs at 70 = 1.44, at a conductor temp of 20 C we need to make sure the resitance is no more than 1.44 x .8 = 1.152 ohms.
 
Thanx.
Another question then ...where i'm working has above average ambient temperatures, do i need to factor this into my maximum Zs values!? Or is this just a factor that effects my Zs reading!?
 
Thanx.
Another question then ...where i'm working has above average ambient temperatures, do i need to factor this into my maximum Zs values!? Or is this just a factor that effects my Zs reading!?

Well if you assume your conductor temp is the same as your ambient, so lets say 35 C

so 70 - 35 = 35 35 x .004 = .14

so 1- .14 = .86 so x the Zs values in BRB by 0.86.

Appendix 14 give you a method which is appropriate which also takes into account the load(operating temp may be lower)
 
your readings will be affected by the ambient temperature. they will be fractionally higher at 30deg. than at 20. the corrected values in the osg are determined so as to be acceptable at 70deg. in other words, say your Zs is 1.15 at 20, 1.44 at 70. it would be around 1.25 at 30.
 

Reply to Maximum Zs values and the rule of thumb in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Replies
4
Views
2K
Got my am2 coming up on Tuesday and I know I have to calculate my Zs readings Maybe I’m overthinking this but am not sure if I need to use the Ze...
Replies
17
Views
3K
Hi All, We have a Merlin Gerin Compact NS100N Single Phase MCCB I've been asked to find its Max ZS Values and to be honest I cant find anything...
Replies
6
Views
3K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi all, Just wondering if anyone can shed some light on the max zs values in the OSG, they don’t seem to follow the 1.25 divisor stated in the...
Replies
10
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock