On page 142 of the latest Guidance Note 3 it list a 16 amp type B max ZS as 2.15, however i think 2.2 is the real value, it also states that at 16 amp type C is 1.1 ohms which is correct, but a type B should be double the value of a type C.

anyone else have a view on this?
 
BS 60898 Type B devices are designed to trip at fault currents of 3-5 times rated current (In). For example a 10A device will trip at 30-50A. Type C devices are designed to trip at 5-10 times In.
we take the worst case of 5 times for type B and 10 times for type C this is how the maximum ZS is calculated . therefore as Z is inversely proportional (Ohms Law) Double the Amps will have to half the impedance Z for the same voltage.
 
Yeah, I think it is wrong, the required current for 16A B curve would be 80A

So 230 x 95% (voltage) x 0.8 (cold conductor) /80A is 2.185 ohm

I think it's been rounded off a bit too much!

Btw a B type will only be double the C type resistance for generic characteristics, once you obtain manufacturers data it doesn't always maintain this "rule" because the instantaneous section of the curve isn't necessarily at 5 and 10x - there is actually a broad acceptable range so you could have a B with 4x, and a C at 11x
 
yes i would agree with that, you could also look at a 32 Amps type B at 1.1 ohms , based on your calculation it looks like that missed the 8 out
 
Yeah, I think it is wrong, the required current for 16A B curve would be 80A

So 230 x 95% (voltage) x 0.8 (cold conductor) /80A is 2.185 ohm

I think it's been rounded off a bit too much!

Btw a B type will only be double the C type resistance for generic characteristics, once you obtain manufacturers data it doesn't always maintain this "rule" because the instantaneous section of the curve isn't necessarily at 5 and 10x - there is actually a broad acceptable range so you could have a B with 4x, and a C at 11x

Wouldn't you assume a conductor AC impedance based on 70*C as that is 1) the worst case 2) reactance is ignored 3) wire gets hotter as the short circuit occurs.
 
Wouldn't you assume a conductor AC impedance based on 70*C as that is 1) the worst case 2) reactance is ignored 3) wire gets hotter as the short circuit occurs.
No

You are measuring the Zs when cold so you have to correct for running temperature.

You need to ensure, in this case it operates at 80A, well at 230V this would be an impedance of 230/80 ohm.

However, the voltage is allowed to be lower than 230V by 5% so to ensure it still operates, you must use 95% of nominal voltage hence 230 x 95% / 80 ohm.

This would be the impedance when hot, but we will be measuring it whilst cold, therefore following the normal accepted figures you take 80% to be the cold value.

This obviously corresponds to a temperature rise from cold (20 degC) to 93 degC

Hence the formula I posted (which is laid out in the standards anyhow)
 
No

You are measuring the Zs when cold so you have to correct for running temperature.

You need to ensure, in this case it operates at 80A, well at 230V this would be an impedance of 230/80 ohm.

However, the voltage is allowed to be lower than 230V by 5% so to ensure it still operates, you must use 95% of nominal voltage hence 230 x 95% / 80 ohm.

This would be the impedance when hot, but we will be measuring it whilst cold, therefore following the normal accepted figures you take 80% to be the cold value.

This obviously corresponds to a temperature rise from cold (20 degC) to 93 degC

Hence the formula I posted (which is laid out in the standards anyhow)

Thanks, that clears it up. I'm used to table 9 chapter 9 which assumes 75*C conductor temps.

One last question... why not -10% voltage?
 

Reply to Maximum ZS values GN3 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Replies
4
Views
2K
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
I work in the events industry which works under 7909. This assumes that someone qualified 7671 etc has tested the distor's and designed a system...
Replies
12
Views
3K
Hi all, Just wondering if anyone can shed some light on the max zs values in the OSG, they don’t seem to follow the 1.25 divisor stated in the...
Replies
10
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock