Hi folks, I’m looking for some advice on a minor problem my parents have with their kitchen lights. They have 2 light fittings in the kitchen each carrying 4 spots and on occasion when one of the bulbs go the circuit breaker trips - there are no RCDs. It only happens in the kitchen (the circuit covers the whole ground floor) and whilst it’s not a huge problem, it’s awkward for my 80 year old parents to get to the CU which is in a kitchen cupboard, groundf level and right in a corner (whoever installed it was a right dimwit).
Any thoughts on what the problem might be?
 
It’s quite a common problem, as the bulb goes the resistance drops and the current increases. This all happens very quickly but B curve MCBs can react and trip.
What sort of bulbs do the spotlights take? It might be possible to put in good quality LED bulbs that last considerably longer and also consume less power. (Don’t bother with cheap ones).
 
As above, the most common reason for MCBs to trip has been filament bulbs blowing as they arc inside, instead of just heating the tungsten wire, and that has a much lower resistance so much higher current.

Occasionally they would take out the old 5A rewireable fuses, but only a very unfortunate case. However, MCB will trip much faster on moderate fault currents so are likely to go in sympathy with the bulb.

If you can just change all the lamps to LED, much less trouble in that respect. If it is for a cosy place make sure you get the 'warm white' type, though for some folks they prefer the 'cool white' as closer to daylight for bright preparation areas.

Also take care if they use a dimmer as not all LED lamps are suitable for dimming so if they need it you will have to look specifically for dimmable ones.
 
Thanks for all the replies, the bulbs are halogen and I was wondering if it may have been arcing across the gas so I advised them to replace with LED’s. Hopefully that will do the trick.
 

Reply to MCB trips when bulb goes? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
My garden lighting was tripping my MCB so I checked all the junction boxes outside. I disconnected the live, neutral and earth connections in...
Replies
2
Views
874
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi The ground floor of my house has two lighting circuits which are each protected by an MCB. One of those circuits is just indoor lights. The...
Replies
15
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock