Discuss MCB's - I2 ≤ Iz1.45 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
1
Can anybody help me with this......I understand the concept of the equation I2 ≤ Iz1.45, however what I’m not sure about is how we obtain I2?

The way I understand it could be either by multiplying In by 1.45 or multiplying In by 5 (which would be the worst case scenario of the MCB’s tripping characteristics 3 – 5).

So which would you use and what is the difference between the two is what I’m struggling to understand, sorry if I wasn’t very clear?

Thanks
 
I2 is the current causing operation of the device and is the 3-5 * In for type B MCBs that you mention, however the regulations state that the I2 <= Iz * 1.45 is deemed to be complied with if using standard circuit protective devices so it is not necessary to ever know I2.
 
Effective operation means regardless of time.

Look at the time curve characteristics in BS 7671 Appendix 3.

For example, A 20A BS 3036 will operate with as little as 40A applied to it.

The fusing factor is the ratio of a fuse's minimum fusing current (the smallest current that will cause the fuse to melt, or I2) and the nominal rated current (usually the number in Amps marked on the fuse body).

BS 3036 fuses have high fusing factors, for example 40A/20A = fusing factor of 2.

The typical fusing factor for a protective device is around 1.45 - 1.8, because the BS 3036 fuse take longer to operate we apply the rating factor, Cf, of 0.725 - which is obtain by diving the 1.45 common factor by the 3036 factor of 2 - when the device is required for overload protection.



I've waffled again.
 
Effective operation means regardless of time.

Look at the time curve characteristics in BS 7671 Appendix 3.

For example, A 20A BS 3036 will operate with as little as 40A applied to it.

The fusing factor is the ratio of a fuse's minimum fusing current (the smallest current that will cause the fuse to melt, or I2) and the nominal rated current (usually the number in Amps marked on the fuse body).

BS 3036 fuses have high fusing factors, for example 40A/20A = fusing factor of 2.

The typical fusing factor for a protective device is around 1.45 - 1.8, because the BS 3036 fuse take longer to operate we apply the rating factor, Cf, of 0.725 - which is obtain by diving the 1.45 common factor by the 3036 factor of 2 - when the device is required for overload protection.
Thank you
 

Reply to MCB's - I2 ≤ Iz1.45 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
827
Hi I'm supervising maintaining a building powered by a 1250 Amps and i had a total blackout twice within a week. Checking the MCB and it's...
Replies
9
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
Afternoon all, I have an issue with the loft socket. When we moved the previous owners had a 2.5mm cable going up from the CU Via FCU however...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock