Discuss MCCB incomers on paneboards in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Hi I have a question which I am sure can be answered by the chaps on here in seconds. Why do panelboards often have MCCB's as incoming devices over isolating switches? I understand this can be useful if the PFC is high at the board and an incomer like this can protect outgoing devices. Is this the only reason though? Is there any other reason? Doesn't the addition of an Mccb just cause discrimination problems with the device protecting the supply to the panel board? Am I missing something? Thanks for your replies.
 
Hi Tony,

i am am talking hypothetically not about an actual installation. Let's say it is fed on a sub main from another MCCB board (not tails at origin and circuit length is over 3m). What is the purpose of the MCCB incomer? I have seen this many times and always wondered. Is it purely due to fault current restrictions on the panel-board/ outgoing ways?

thanks
 
One example is where the sub main is a fair old length and therefor oversized and wont fit a 125a db isolator, ie anything over 50mm2.
 
One thing, I hate is the use of “panel board” it’s an Americanism. Distribution board or just board if you don’t mind.

You mentioned discrimination, our companies policy was as follows:

For a sub board fit an isolator and rely on the main boards outgoing OCPD to protect both the cable and the board’s busbars.

If the board is fed off an intake busbar chamber use a MCCB for the incoming as it will be the OCPD for that board.

The bottom line is, where is the board fed from and what protects the feeder? To fit an MCCB in series with the circuit OCPD is nothing but a waste of money.

Larger cable sizes can be accommodated by termination adaptors. It’s not a reason to fit a MCCB in series with the OCPD at the origin.

There is the odd occasion that E/L protection is required for a board, then a suitable MCCB incorporating E/F as the incoming is be fitted. Definite indication the fault is related to the board and not the cable. It was the only time we deviated from the above. I could count on the fingers of one hand the boards I’ve fitted with E/F protection.
 
Tony,

Thank you for the information. Very Useful for my understanding. Sorry for my poor terminology, I shall use the term 'MCCB board' in future.

The bottom line is, where is the board fed from and what protects the feeder? To fit an MCCB in series with the circuit OCPD is nothing but a waste of money.

What you describe above is what I have seen on may of the jobs I have worked on. I think this may be because the jobs I work on are mainly consultant designed and therefore are over specified? I think I will suggest to my gaffer that we suggest changing to switch isolators on future jobs for a cost saving (on conformation that OC protection is not required because it is afforded upstream).

Thanks again,

JameZZZ
 
Last edited:
Some main switches/isolators look very much like MCCB's but have no Over Current Protection within them, they just use the same frame casing as the the MCCB's of the same manufacturers range.

In some cases, depending on the distance from the main distribution board (MDB) or whether the MDB is in a locked or restricted location, it may well be prudent to provide a MCCB or other means of OCPD at a sub/final distribution board!! If it's of an adjustable MCCB type, then the parameters can be pretty much set to cover the DB needs while ensuring discrimination with the up stream feeder OCPD!!
 
Hi E54,

The are definitely MCCB's (60947-2).


If it's of an adjustable MCCB type, then the parameters can be pretty much set to cover the DB needs while ensuring discrimination with the up stream feeder OCPD!!
They are always adjustable and wound down. This must be the thinking.

Thanks very much,

JameZZZ
 
Not the way we’d do it but every competent person had access to every part of the system.

I always forget about restricted access switch rooms. We would regard that as unsafe, access could be required at any time in an emergency.
 
I've used MCCB incomers where a board has been supplied directly from a rising busbar in a tower block.

If I recall correctly, even Eaton (MEM) call them panel boards, but I agree that it's not the best name for them!
 

Reply to MCCB incomers on paneboards in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Would any fellow electricians consider using an open PEN device to protect a metal trailer used as a "Canteen". It is likely to be often connected...
Replies
3
Views
297
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
Hello, Not an electrician and I currently live in an apartment building. Over the past few years I have been having abnormal problems with my...
Replies
2
Views
712
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock