Trying to extend the 2 output wires safely(around 2 metres),i don't have much previous experiences with electrical appliances but I Did some research and I need a wago connector block possibly 2

Which rated blocks are suited ? I don't know if the 36a gets split in half on the outputs

The job is a simple one , but I want to make sure everything is matched correctly

Thank you for your time

Highest Regards ,Lee.
 
This driver produces 36V at up to a little over 4A - any Wago connectors that are suitable for the stranded cable will do (lever type). The connections ought to be enclosed e.g. in a Wagobox.

And you need a separate Wago for each of the 2 wires - join the output wires together in one Wago and it will likely either shut down or blow up.
 
You could use two Wago 221 in-line splicing connectors, which as said above are suitable for stranded wire, and use 1mm or 1.5mm csa flex to extend for just a couple of metres.
Edit - maybe actually four Wago's will needed, two at the Meanwell end and two at the lighting end!
 

Reply to Meanwell driver elg-150-36a in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi all, Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation. We've been putting in a new kitchen into an...
Replies
17
Views
2K
Moved into a refurbed flat a couple of years ago and there were a few suspect things about the electrical work which I’ve not got round to...
Replies
8
Views
2K
Left over stock, all brand new unused in boxes. Looking for £150 job lot. £10 postage or can be collected Description: ELG-75 series is a 75W...
Replies
0
Views
820
Last time I posted on forum it was on the thorny issue of over unity machines which alas got confused with perpetual motion -- and other supposed...
Replies
72
Views
8K
A
Before I begin, I put my hands up and admit I'm neither a sparks by occupation, nor a qualified domestic installer, nor Part P qualified. I do...
Replies
4
Views
23K
Boatelec
B

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock