"You can measure the earth leakage by using an earth leakage clamp meter and clamping all the phases (and neutral if there is one) simultaneously."

That is the kind of thing I was looking for, I just can't find one!


All the kit I can find clamps only the earth (which I would assume is only useful for single phase with no potential parallel paths).



"
or proper training coupled with an effective preventive maintainence program....

what do you think?" That would of course be prefered, but sometimes we have to be realistic


As ever I am explaining things poorly and only giving half this info to try and keep the conversation on track. e.g. discussing whether RCDs are the best solution is irrelevant, the boss wants them in, they are going. discussing whether feeding one machine of the next is a good idea, we all know it's- the boss wants it that way so its being done like that.

I really do just need help on the bit i asked for.

I'm wanting something like Marvo described. Does anyone know where to get one, or who makes them?

Thanks,



 
Last edited by a moderator:
Where is the factory in question, I only ask because there are a lot of very knowledgeable guys on here and maybe would be willing to design the system for you, don't know how much that would cost your boss but it will be cheaper than lost production due to you designing it wrong.
 
Why are they on plugs and sockets? Factory machinery is much safer if it's fixed and hard wired.

Most of the equipment will be hard wired. Some parts of the production line get changed, they will be on plugs/sockets


The boss only wants them until the day the first one trips.

I know, hence wanting that not to happen unless it is stopping someone getting a shock


It isn't the job of an electrical designer to prevent or protect against reckless or negligent behavior or willful damage by the machine operator.

Designs have to take into account usage. The usage here dictates much higher standards of safety. Let me cite an example of retard. They want to use a labeller on a production line. So some idiot runs an extension lead across the floor. Some other idiot runs a POWERED pallet truck over it. It sticks on the wire, so they rev the motor and grind down to live. The metal pallet truck then went live. Due to my insistence that socket was protected by an RCD and no injury was caused. So hiring intelligent people would be preferred, but if you are dealing with retards, you have to take extra care. It's like designing electrics in a farm, this place is populated by large dumb animals who do not understand electricity.
 
Why are they on plugs and sockets? Factory machinery is much safer if it's fixed and hard wired.


The boss only wants them until the day the first one trips.


It isn't the job of an electrical designer to prevent or protect against reckless or negligent behavior or willful damage by the machine operator.
some plugs are interlocked...by means of the isolator switch...
 
Hi,

I have been tasked with rewiring most of the machines in a factory.
Due to the age of the equipment and usage I believe residual current protection is a good idea.

This presents an issue with how they want them wired.

Currently we have cables hanging from the ceiling at multiple points of the production line.
The want rid of this and want each machine in the production line to power the next.

My idea is to fit a dist board at one end and feed them off each other.

The only issue I have is what do I rate the RCD as?

The easy approach is to fit a 30mA RCD as the incomer and feed everything off individual mccbs.

However I do not know if these machines will cause nuisance tripping.


So the short version of this question is how can I measure the residual current on a 3 phase machine?

I've seen a PAT tester that could do single phase, but nothing for 3.

At the moment, the best idea I have (which sucks) is to get a settable RCD and keep reducing the current until it trips. This obviously does not take in to account any fluctuations in the device!

So do any of the sparks know how to do this properly or have any advice to offer?

Thanks,
incidentally for testing 3 phase equipment you need plugs that are wired internally...both in star...and delta....depending on whether or not a neutral pin has been provided.....dont forget that a pat tester measures all live conductors to earth on IR....
 
I take it #22 is not an option
 
Breaking news
Fork truck runs over extension lead



"Unfortunately, just one of those things we can't protect against"

I just wish there was some way we could
icon11.png
icon7.png
 
If you are being told to fit RCD protection use something like this

Earth Leakage Relays

fit one for each machine on it own dedicated feed (if required) and set to maximum setting (30A) and maximum time delay. You will have fulfilled the instruction you have been given and shouldn't get nuisance tripping.
 
Last edited:
Wow lots of questions at once.

Reason for RCDs, many.
For a quick answer.
These will be fed off plugs and sockets, regs indicates RCD requirement.
Boss wants RCDs.
Operators are a f£$^%ing liability and are so reckless with equipment everything in this factory needs RCD protection.
No reason not to add additional safety, if something is designed correctly, it won't cause an issue, but stop an accident.

"and i smell a cascading feeds epic here as well..." - Each piece of equipment will have it's own dedicated feed. Not sure what you meant though, so care to expand?

"
What happens when one machine packs up, it takes out another 3 or 4 or whatever? " That's a good thing. If one item on the production line has an electrical fault the production line stops.


Des, I know little about mining, so your references are lost on me.
Basically a packing machine. Main boxer -> conveyor -> metal detector -> conveyor -> weigher -> LS.


RCDs are going in, no choice on that.
I need to know how to design to avoid nuisance trips.

So what does he suggest you do?
 
"So if I fit an RCD its ok to wire my factory in extension leads ?"

Clearly not, however if you have to deal with stupid people it means they are less likely to be able to hurt themselves.


"
So what does he suggest you do?" - He is a mechanical engineer.

 

Reply to Measuring residual current. How do I know what RCD to fit? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
913
Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Replies
5
Views
2K
There are 2 inverters feeding into a dorman smith C16 rcbo , every time I visit this site (communal area power) it has tripped. it switches on...
Replies
13
Views
2K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi all So had some issues lately related to high current fittings .. dp switches mostly. A number of electric boilers of various ratings .. from...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock