Discuss Megger 1730 erratic readings in the UK Electrical Forum area at ElectriciansForums.net

J

Jaxo

I recently bought a megger 1730 and i`m getting some weird earth loop readings using the no trip function. I know they can be a little higher at times when taking a "no trip" reading as my old 1552 was always a little higher too but these seemed well out...

I only got the meter this week (Used from ebay, but in as new condition). I did a few tests around the house and all seemed fine, Then today I had to use it to test a rewire I did in Belfast and thats when I noticed the odd readings..

ZE: 0.28Ω (which I did think was a little high, but within the limit for a PME all the same)
R1+R2 0.17Ω
Earth loop 1.03Ω

This is just one circuit, but they all seemed to give high readings.. I didn`t bother shorting out the RCD`s to take high readings and compare.. It was a friday and I wanted to get home ;)

I had a google in work and some where saying it could be the 500Ma leads and others saying the batteries etc and I did notice the batteries where near dead.. When I got home I charged it and took a few readings around the house and all seemed fine, ZE 0.11Ω , R1+R2 0.41Ω, No trip earth loop 0.61Ω ...

Strange.. anyone else having these problems with the 1700 series Meggers?

The meter is like new, infact there is not a mark on it,.. It didn`t however come with a calibration cert so I`ll need to go in and get checked but just concerned I may have bought a duff one...
 
When the batteries become low then the readings provided by these meters are not reliable, I would expect this is what happened.
However it is possible that there was a high resistance RCD or MCB in the board that was bumping up your readings.
As you say the no trip test is somewhat variable anyway.
 

Reply to Megger 1730 erratic readings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
319
Hi I've got a megger mft 1720 that I was hoping any one can shed any light on When performing continuity tests (even when nulling the leads)...
Replies
13
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Chaps - having problems with a new Megger MIT420/2 insulation/continuity tester 'oscillating' and failing to give stable resistance readings in...
Replies
2
Views
635
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
605

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock