Hi,

I have a Megger mft1720 and the low current loop test isn’t working properly. Just wondering if anyone else has had issues?
Readings are stupidly high compared to the high current test, and this can be made even worse if there’s an rcd in line......
 
RCD uplift is a known issue when loop testing. If your R1+R2 is good and so is your Ze then just add both together.
 
Thanks for quick replies guys. Was using original Megger leads and bought a new cheap set to try out as well. Have been testing domestic stuff and never used to have a problem. For example today high current Ze was 0.16, r1+r2 for cooker circuit was 0.24. Low current Zs was something like 2.25!!
I have been adding Ze + R1+R2 together for my certs but only as I have no choice atm. Calibration not due til October.
 
cotton bud with switch cleaner on the 4mm sockets. also check no-trip ZS using 1363 plug lead, see if that's high as well.
 
I had the same issue with my megger a couple of weeks ago, turned out that although the neg lead looked like it was fine it had detached slightly inside the probe end and would still work if you pushed the lead into a terminal but give a high reading, I finally realized when I put a crock clip on it and tried to loop at a light and it kept saying no neutral connection! It really bugged the sh@t out of me all morning thinking me tester was kaput and would have to get it repaired, it was only calibrated 2 weeks previously!!
 

Reply to Megger loop impedance irregularity in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Hi I've got a megger mft 1720 that I was hoping any one can shed any light on When performing continuity tests (even when nulling the leads)...
Replies
13
Views
2K
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
595
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
315
Hi guys & gals, I gave in and bought the new Megger MFT-X1. Got my hands on it Friday night, had a little play with it, used it at work on Monday...
Replies
10
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock