    Evening all,
    Need some opinions on this one please:
    TNC-S house, complete new install, all going to plan, nearly finished second fix, customer then arrives with a huge metal lamppost (bought from Frinton-on-sea promenade...) and wants it hooked up in the back garden.
    What is the general consensus on this - my concern is: in the event of loss is supply neutral, everything connected to MET, including that lamppost, will rise to a voltage, anyone touches it may get a shock?
    Or, will the fact it's planted in the earth keep any possible voltage down?
    Am I making something out of nothing here or would this be safer as a TT?

    Any thoughts welcome.
     
    • Winner Winner x 1
  2. westward10
    Online

    westward10 Ugly kids what a disappointment. Electrician's Arms

    Location:
    Northamptonshire
    What is it with this neutral loss, in the house no one bothers but go outside and there are shouts of ROD IT.
     
    • Agree Agree x 5
    • Bad Spelling Bad Spelling x 1
    Last edited: May 19, 2017
  3. weevilward
    Offline

    weevilward Active EF Member

    Location:
    United Kingdom
    Ok, so touching a radiator bonded in the house in no different to touching a lamppost bonded in the garden? Is that what you're getting at?
     
  4. weevilward
    Offline

    weevilward Active EF Member

    Location:
    United Kingdom
    Ok, so touching a radiator bonded in the house in no different to touching a lamppost bonded in the garden? Is that what you're getting at?
     
  5. Flanders
    Offline

    Flanders Regular EF Member

    Location:
    Tamworth
    Im think there is somthing in special location for lamp post but it may be relating to street furniture
     
  6. Leesparkykent
    Offline

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    The post will propably act as one big rod.
     
    • Agree Agree x 1
  7. westward10
    Online

    westward10 Ugly kids what a disappointment. Electrician's Arms

    Location:
    Northamptonshire
    Most lighting columns on the highway are PME they seem okay.
     
    • Agree Agree x 2
  8. weevilward
    Offline

    weevilward Active EF Member

    Location:
    United Kingdom
    So I'm reading too much into it.
    Thanks fellas. Never thought twice about domestic outside lighting before, but when something different comes along it makes you think twice...
     
  9. Richard Burns
    Offline

    Richard Burns Trusted Advisor

    Location:
    Cambridgeshire
    Business Name:
    Richard Burns
    This is probably a case of minimal risk. In general you are not constantly handling a lamppost, as opposed to hand held electrical equipment, and so the risk of neutral loss fault occurring and it being a risk due to contact are low.
    Bonding will have limited effect since the potential you are trying to eliminate is between earth and the supply and bonding will only limit the PD between the MET and the supply.
    Within a property there should be no potential differences because the bonding connects all sources of potential difference together. Outside a property without installing conductive mats in the ground you cannot avoid being in the presence of a nominal 0V from true earth and so the risk is increased.
     
    • Like Like x 1
  10. Paul mccullagh
    Offline

    Paul mccullagh EF Member

    Location:
    Cambridgeshire
    Run swa to the lamp post (volt drop calculations) bonded on a 30MA rcd in the consumer unit job done!
     
  11. westward10
    Online

    westward10 Ugly kids what a disappointment. Electrician's Arms

    Location:
    Northamptonshire
    Why would it require rcd protection.
     
  12. westward10
    Online

    westward10 Ugly kids what a disappointment. Electrician's Arms

    Location:
    Northamptonshire
    This was suggested many years ago by the ILE but was felt the column would be unreliable as an electrode due to corrosion, protection on the column to prevent corrosion and the means of bedding it in the ground.
     
    • Like Like x 1
  13. weevilward
    Offline

    weevilward Active EF Member

    Location:
    United Kingdom
    It doesn't need RCD but it wouldn't hurt to have it.
    Yeah this one is pretty rusty!
     
  14. weevilward
    Offline

    weevilward Active EF Member

    Location:
    United Kingdom
    Thanks Richard, this makes sense.
     
  15. Paul mccullagh
    Offline

    Paul mccullagh EF Member

    Location:
    Cambridgeshire
    I would personally protect this with a rcd due to someone dismantling fixtures and changing a light bulb!
     
Loading...
Similar Threads - Metal lamppost garden Forum Date
Dual Dry line boxes & metal accessories Electrical Tools and Products Yesterday at 6:01 PM
Metal Light Switch + Plastic Back Box with no earth terminal Electrical Wiring, Theories and Regulations Jul 3, 2017
Code cables in walls with metal partitions Electrical Wiring, Theories and Regulations Jun 28, 2017
Metal CableTie Tensioner Electrical Tools and Products Jun 16, 2017
New metal roof on existing concrete garage Electrical Forum Jun 16, 2017
Plastic face plates fitted to metalled back boxes Electrical Forum Jun 6, 2017

Share This Page

  • Electricians Directory Post a Domestic Job Post a Commercial Job