Discuss Metal light fittings. in the UK Electrical Forum area at ElectriciansForums.net

It's always a qualified spark supposedly. Usually described as "a proper electrician" but the clown didn't know what he was doing, if he ever existed.
I'd be willing to bet there were no certs or notification either.
 
That's £1200 house rewire for you, using a Mains board that's been in stock for a few years. No test certs no paper work. No cares. Please keep us updated. And no i wouldn't of changed the fittings
 
Thanks for the replies. The owner has contacted the original installer. Will be interesting what they have to say. Probably end up sorting out for them. We will see. Were not all cowboys in Cornwall lol :)
 
Not disagreeing with any of the previous posts here, but, ......There are plenty of metal light fittings around that are manufactured to Class 2 requirements.
 
If no Rcd was fitted,the chances are the installer was a potcher who knows "a lot about electrics"

Nothing new in that,except these days he may be signed up as competent
 
Not disagreeing with any of the previous posts here, but, ......There are plenty of metal light fittings around that are manufactured to Class 2 requirements.

Very true, but in a deathtrap like that common sense and risk management says just walk away. I wouldn't have fitted anything there. Problem being, what you do may not have made the situation any worse, but when someone gets electrocuted the name of the last person who worked on it is you so guess who ends up in the dock.

My question would be, is one under a duty of care to notify Building Control about it? If so, moral or statutory duty?
 
no RCD on a TT is an instant 2....so you wouldn`t be carrying out any work until adequate fault protection was in place...would you.

this could take the form of 100mA s type mainswitch with 30mA RCDs for the finals coupled with decent TT earthing arrangements (deep rod/s) for good, stable values of Ra..

just out of interest what was the Zs on the circuits in question?
 

Reply to Metal light fittings. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
641
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
697
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
657
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
448
Hi all, Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation. We've been putting in a new kitchen into an...
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock