Discuss Meter Tails : Do i have a potential issue? in the UK Electrical Forum area at ElectriciansForums.net

clanky

-
Reaction score
17
Hello again,
Was looking at installing yet another dedicated consumer box for my EV charger off the henley blocks and i noticed that a meter, which was installed a couple of years ago (outbuildings on the second phase of a split phase supply) has been wired with 16mm tails but with a 100a isolater switch post meter. Should these have been 25mm? The installer (plumber who'd been on a meter course apparently) had no idea what i was going to install downline of this meter so shouldnt have he erred on the safe side?
 
No, the 100A refers to the maximum rating of the switch. Assuming some normalcy here, 16mm tails are rated to 99A so I'd suspect you probably have an 80A incoming fuse.
 
100A isolator or cutout doesn’t mean anything except it is rated at 100A maximum. Fuse could be 60a or 80a. If so, tails are fine.
 
Just checked and the main fuse is 100A...one in the middle.
 

Attachments

  • fuse.jpg
    496.7 KB · Views: 48
Hello again,
Was looking at installing yet another dedicated consumer box for my EV charger off the henley blocks and i noticed that a meter, which was installed a couple of years ago (outbuildings on the second phase of a split phase supply) has been wired with 16mm tails but with a 100a isolater switch post meter. Should these have been 25mm? The installer (plumber who'd been on a meter course apparently) had no idea what i was going to install downline of this meter so shouldnt have he erred on the safe side?
Are the tails running or proposing to run through the fabric of the building ?
 
I’d be more worried about the fact that we have plumbers telling people they’ve been on a meter course and tamper with mains electricity
Apparantly it was a 'thing' with the rollout of smart meters. If you were corgi registered then the suppliers would train you up for electric meters so you could do both in one visit.
 
Apparantly it was a 'thing' with the rollout of smart meters. If you were corgi registered then the suppliers would train you up for electric meters so you could do both in one visit.
Never heard of it

Asking plumbers to do mains electricity sounds like a recipe for disaster. Whoever thought of that idea needs to be sacked. We as electricians aren’t even allowed to touch the meter
 
Never heard of it

Asking plumbers to do mains electricity sounds like a recipe for disaster. Whoever thought of that idea needs to be sacked. We as electricians aren’t even allowed to touch the meter
This was 5 years ago so maybe things have changed since then. But whatever, nothing surprises me anymore. I lost a job once to a brazilian who'd done a 2 month 'mechatronics' course, I had 15years experience and a degree. Money talks.
 

Reply to Meter Tails : Do i have a potential issue? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Client has had a meter installed for a new consumer unit in their shop they are looking to rent out the spare space for a barber shop so they want...
Replies
10
Views
311
Hi, I was hoping someone with a little more insight might be able to shed some light on a potential issue I have, as I can't seem to find another...
Replies
75
Views
7K
  • Locked
My house was built in the 1930s, The fuse in my service cut out is 60Amp and the wire coming from the street has a 16mm2 copper core(easy to see...
Replies
12
Views
572
I have a client who wants an EV charger installed, charger TBC, but about 7KW, installed about 20m away from this installation. I've not done one...
Replies
37
Views
3K
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock