Hi guys
I'm installing a CU in a new build and have a couple of questions I need some guidance with regards to the meter tails.
I need to drill a hole through the wall (for the meter tails) to access the main supplies which are located in the recessed box on the outside of the property. I am going to use 25mm tails. My question is the tails will be ran in a stud wall to the CU but my concern is they are not protected from nails screws in wall etc. Do you guys used armoured cable? Cant imagine many people carrying round 3 core 25mm cable? Also are meter tails ented the CU via rear entry or do they have to be secured to CU via cable gland?
Thanks for the help
I'm installing a CU in a new build and have a couple of questions I need some guidance with regards to the meter tails.
I need to drill a hole through the wall (for the meter tails) to access the main supplies which are located in the recessed box on the outside of the property. I am going to use 25mm tails. My question is the tails will be ran in a stud wall to the CU but my concern is they are not protected from nails screws in wall etc. Do you guys used armoured cable? Cant imagine many people carrying round 3 core 25mm cable? Also are meter tails ented the CU via rear entry or do they have to be secured to CU via cable gland?