Discuss Metrel MFT mi-3152 RCD test in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

John-

-
Reaction score
48
Hi
Recently invested in one of these. Impressed! Until...

i came to test my 100mA type A RCD. Long story short, it would not test correctly until
I set it to Type AC, rather than A. My Mega MFT worked fine, only as it is so old it has no options for S type. I did try all the settings in the individual and sequntial test mode.

Anyone else have this with their Metrel 3152?

i will call Metrel on Monday to confirm.

cheers

john
 
So i called Metrel. I updated my firmware. Still getting the same issue. The RCD goes beyond 500ms and does not trip when set to Type A. It is a type S, with a fixed delay of between 200 - 300ms, accordimg to the data sheet. Yes i am also setting to type S.


Looks to me like the Metrel tester has an issue with S type on type A (pulsed DC) as it trips at around 340ms when the tester is set to type AC. I even bought and installed the same RCD to check that it was not the RCD at fault - i get the same issue.

i have filmed it and will send to both MCG and Metrel over the weekend. Will update thread as and when.

it also seems to
Me that the tester does not go up to 1 second, max aloud for TT distribution circuits. Raised this but not heard back.


Cheers

john

ps i am disappointed with battery life. The tester will not last a full day without further recharge or another set of batteries...
 
Update...

MCG (CEF) really lightning fast about pulling one for factory, checking it, asking about batch codes etc and confirming they see no issues at the factory end.

Metrel however... The tech support guy i spoke to was very helpful, it has been logged in Jira system but... I have had no update on progress... Twice asked and twice the same response, it has been escalated to technical.

Update again soon, but looks to me like a bug or two in the tester, one of which is it only going up to 500ms...
 
Ok. Final update.

in summary it was the RCD! Or I should say both MCG S Type RCDs that i tried.

Metrel carried out a test and filmed it. For them the Type A test worked, it passed. However, only just! The test will allow up to 500ms for a pass in accordance with the manufacturing standards. The test came out at 470ms…

it should be around 230ms, according to MCG blurb.

Any way. I installed a more expensive Hager S type 100ma A tyoe RCD and this tested out perfectly.

Moral for me, avoid MCG S type RCDs. I use their A type 30mA RCBOs, and do not have the same issue.

MCG have not resonded further. I am still waiting for an update from Metrel on other issues i have…
Cheers
John
 

Reply to Metrel MFT mi-3152 RCD test in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
659
Hi guys & gals, I gave in and bought the new Megger MFT-X1. Got my hands on it Friday night, had a little play with it, used it at work on Monday...
Replies
10
Views
3K
Hi all, Just done an EICR and all tested fine, until I got to the RCD's. It's a dual RCD board, not sure if it's TNCS or TNS as it's a top floor...
Replies
8
Views
1K
I'm fitting one of the Apex 7S units on Friday. I'd avoided the original range after a couple of bad experiences but I figured a new model might...
Replies
6
Views
782
Testing an Ashley & Rock BS4293 RCD Type AC (CU dated 1989, property built c. 1990-91) this morning with a Metrel 3152 on RCD Auto; x1 and x5 were...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock