TheCodboy

-
Arms
Reaction score
109
Hi all,been to look at flat today and it requires a new Consumer unit. Its an old porcelain type of fuse holder and shield and some of them are damaged. The flat is in one of these 60's built blocks with a meter cupboard on each floor. In the meter cupboard is the service head, meter and an isolator. From the isolator is a 6mm 2 core pyro leading to the flat. The main earth is taken from an earth clamp on the pyro pot,looks to be 2.5mm There is absolutely no sign of overloading, heat or anything like that. My MFT is being calibrated at the moment so i couldn't take any readings,but i did do a visual check in the board and at sockets etc and as i say, no sign of thermal/overload trouble. 2 bed flat with a small kitchen so don't think there's a great deal of load. So, realistically there's no way of upgrading the tails, would you guys be happy to install a new DB with these tails? I'm going to ring Napit tomorrow, but i would like to hear what you guys have to say. Many thanks.
 
Is the isolator fused, what length is the pyro?
It doesn't appear to be fused. From the meter cupboard roughly 6 meters give or take.
[automerge]1593622414[/automerge]
if that MICC tests OK, and is adequate for the load, no reason not to use it
My thinking is that i can only improve the condition of the install by adding rcd protection etc. The service head fuse carried says 60/40a I know that its whats inside that counts but there's a good chance that hasn't been touched since day 1.
 
If its more than three meters it should be fused. Are the earth connections to the pyro OK? I tend to agree with Tel that if it tests ok it will be fine. but it should be fused and the earth needs to be checked.
[automerge]1593622532[/automerge]
Pyro has an earthed sheath and dosent necessarily require an RCD.
 
But only 51A if bare, exposed, clipped direct, because the circumference is smaller so less surface area in contact with the air.

However, you mention a 1960s build date, in which case it's surprising that the cable is metric. Does it actually say 2H6?
 
It says 6mm on the cores

That doesn't necessarily mean much, check the markings on the gland or pot.
I've seen 6mm stub sleeve used 1.5mm before.
[automerge]1594243515[/automerge]
Yes I wouldn't hesitate to use MICC as long as it is in acceptable condition.

I wouldnt accept a BS951 clamp as the means of connecting to the sheath for a CPC though, they aren't designed for that purpose.

In the past I have dealt with this situation by wrapping a copper strip around the cleaned sheath with a tab sticking out and soldering it in place, then bolting a lug to the copper strip.
 
But only 51A if bare, exposed, clipped direct, because the circumference is smaller so less surface area in contact with the air.

However, you mention a 1960s build date, in which case it's surprising that the cable is metric. Does it actually say 2H6?
2D3AC53D-33E9-45C5-B354-4E5D102BB03F.jpeg

2h6 on the pot
 
Here's one I did a few years ago, (with the correct permissions from the BNO) moved and reterminated an imperial 2 core feed to a flat.
As per pyrotenax's advice the nearest size metric pot was soldered onto the cable. I made the earth connection and the clips from copper strip (I keep stuff like that in one of my toolboxes as I often seem to end up dealing with such things)

IMG_20181204_132916.jpg

[automerge]1594281830[/automerge]

Those couplers with the earth terminal are a rare beast these days, and when you do find them they are not so substantially made anymore!

So it is indeed metric cable, that puts the date of the installation later than the 60's as metric cable came in in the early 70's
 

Reply to Micc tails from meter cupboard in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

DNO ripped out antique main incomer/breaker .The guy hated us and himself and everyone else by the end of the job ! . Client going to contact...
Replies
21
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
829
I really hope someone can help me. Last July I got an electricity bill showing an enormous rise in my kwh consumption of about 900% from what it...
Replies
11
Views
2K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Good evening all, So been to an upstairs flat today I East ham, the entire road is terraced 2 storey building which look like a row of terraced...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock