Discuss Move light position? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
362
Extension wiring.

Included in this was some wall lights, and with the shape of the extension, drop from ceiling is about 3 meters. Cables have been in for weeks, dot and dabbed and plastered. Lights were positioned in the middle of a wall at 2m height from floor. Now customer asks 'can you move the light 150mm to the left as they want to put a bookcase against one wall, in which case light won't look like its in the middle'!

If I move the light then cables are not in safe zone anymore!

What would you do?
 
What are the chances the bookcase covers the original position thus allowing you to put an empty patress and blanking plate in the original light position thus maintaining the safe zones?
 
Or is the wall less than 100 mm thick and maybe possible to put a patress on the other side of the wall? This won't ruin the clean look on the light side and still comply
 

Reply to Move light position? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
754
Hi all! Posted on here a couple of years ago and got great advice. Have been self employed a couple of years now and always find pricing work the...
Replies
10
Views
3K
Hello, We changed plans with lighting in one zone. Now instead of 4 downlights (square shape of 1400mm side) we want a chandelier. Since...
Replies
2
Views
867
I'd appreciate the wisdom of the find minds here regarding this job. Yes, I've drifted into Wales again.... An extension is being planned as...
Replies
4
Views
936
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
921

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock