Discuss Multimeter tripping rcd... in the UK Electrical Forum area at ElectriciansForums.net

N

Newbie90

Hi all,

I have a Fluke digital multimeter and whilst testing live to earth on a controller, it tripped the rcd.

Can anyone explain why?

Is it like the fluke t120 voltage indicators where you have to test between live and neutral for 5 secs beforehand?

Thanks
 
Should be a low current test, if it is and its still tripping try reversing the polarity of the test, ie live down earth and earth down live, some of the new rcds have this problem and reversing the polarity seems to solve it, also make sure there are no loads on the circuit
 
i would hope that you were measuring voltage, not current. it would seem that the meter is drawing sufficient current to trip the RCD.
 
Can't believe a digital multimeter would draw enough current to trip an RCD, my money's on the 'using it as an ammeter' theory. Daz
 
When you say it has to be held on live to neutral for 5 seconds is that for the continuity buzzer to work. I had an alphatec that would trip rcds If you tested on live to earth before live to neutral as charging the internal capacitor that powered the buzzer drew enough current to trip most rcds. Useless it was and had a very short spell in my toolbox.
 
Can't believe a digital multimeter would draw enough current to trip an RCD, my money's on the 'using it as an ammeter' theory. Daz

Yes my fluke multimeter 117 has LoZ function to prevent phantom voltages from being displayed, I think I might try it tomorrow to see if it trips the rcd on L-E test.
 

Reply to Multimeter tripping rcd... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
349
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
589
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have...
Replies
25
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
811

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock