Discuss Mystery cable in receptacle box in the DIY Electrical Advice area at ElectriciansForums.net

ndrose

DIY
Reaction score
0
I am replacing some of the old receptacles in a 1940s house. Armored BX cable, two conductors, cable is the ground. Mostly pretty straightforward.

One box contains a problem. Two cables coming into the box. Black and white from one cable attached to the receptacle. Other pair taped up.

The receptacle works fine—that pair is ok. But I wanted to know what the taped pair was. Tested for voltage.

Known hot to known neutral (just to be sure): 110V
Mystery black to known neutral: 0V
Mystery white to known neutral: 0V
Known hot to mystery neutral: 110V
Known hot to mystery black: 55V

Not sure how to interpret that. I had expected it to have fed something decommissioned downstream, and that it would be 0 to everything. That’s obviously not the case. But I don’t know what it is.

Thanks for any help
 
My speculation so far:

The mystery cable can’t be a source since there’s no voltage to ground from either conductor.

The white conductor must have a path to ground, and the black conductor a partial path to ground.

If the cable went downstream to a decommissioned fixture, maybe whoever disconnected whatever it was left the conductors free in the box, and just taped up the source end, in the box I’m examining. Suppose the white is in full contact with the downstream box, the black in poor contact. The metal boxes and BX armor would provide a path to ground from there.
 
My speculation so far:

The mystery cable can’t be a source since there’s no voltage to ground from either conductor.

The white conductor must have a path to ground, and the black conductor a partial path to ground.

If the cable went downstream to a decommissioned fixture, maybe whoever disconnected whatever it was left the conductors free in the box, and just taped up the source end, in the box I’m examining. Suppose the white is in full contact with the downstream box, the black in poor contact. The metal boxes and BX armor would provide a path to ground from there.
It sounds like just a cable that’s not supplying any loads anymore.
 

Reply to Mystery cable in receptacle box in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello everyone... There are a total of 4 cables entering the junction box at the top of the staircase. Two 12/2 cables are coming in through the...
Replies
1
Views
440
L
WIRING FOR WALL SMART SWITCH FOR CEILING FAN/LIGHT Just bought a smart wall switch for a ceiling fan/light currently connected to a single switch...
Replies
0
Views
723
littletwinn
L
Before I pay an electrician to come check my work, I thought it worth a post here. I don't want to pay the cost of a small car for a whole-house...
Replies
0
Views
1K
I have a light that runs off a single switch. In the same box as the single switch there is a now abandoned three wire cable running to another...
Replies
3
Views
1K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
534

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock