Hi all,
After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone.

Customer wants to upgrade from rewirable CU to RCBO so fairly old wiring but no signs of cable breakdown or anything totally messy on inspection. This circuit basically holds everything inc. boiler etc but exc. lights and cooker.
Ring continuity tests are slightly messy but well within limits.

IR testing L/N & L/E = approx 150M, however N/E = dead short @ 0M

Unplugged everything, isolated all FCUs that I can find but still no luck. Temporarily tried the circuit on a RCD to check I hadn’t missed any loads or just being an idiot but it only holds for a minute or two before it trips confirming a fault.

My thoughts are to now break down the legs of the ring and go hunting the fault similar to finding a continuity fault.

Any one have any other options or go to places to start that might speed up the process??

Cheers in advance.
 
Were all the ring conductors disconnected when you did the IR test? (I know the CPCs should technically be left connected during this test, but we're talking fault finding here).

Out of interest, what does it read if you test using the low Ohms range of your tester?
 
Is there an immersion heater?
Also, checking an obvious question, you had the Neutral's disconnected at the CU when you did the test showing 0 N-E ?
(just double checking you aren't measuring the TNCS link, or indeed another circuit could have the fault)

Otherwise - yes - break ring somewhere and see which half it's on.
 
Sounds like it's going to need the ring circuit splitting.

I'd still test it on the low Ohms range though to see what actual resistance you are talking about here. Remember the MR range will show 0R but it probably won't actually be that.
 
As @DPG says, if it can be detected on a low resistance continuity test it might speed things up. Leaving the CU ends disconnected and measuring at each socket until you find the two lowest L-E readings. In theory it's between them if neither of them are spurs.

Best of luck. You'll get there in the end. If you reach an understanding of the problem in under 2 hours you'll have done well!
 
If it's a conventional ring just make an educated guess where the mid point is and split it there, and test each leg from the CU. That should rule out half the ring. Split the faulty leg at its mid point, test again. Keep going till you run out of places to split it and you will have hopefully found the fault, or at least be close. It's the most efficient way, known in other fields as a "binary search".

If on the other hand it's a DIY disaster zone like the one I had last week, which was a figure of 8 bodge with spurs off spurs off spurs you're in for hours of fun. Eventually traced it to a choc block plastered into a (now slightly damp) wall.
 

Reply to N/E fault IR=0 - RCD won’t hold in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all , after some opinions on N-E fault or ring main. After chasing this fault and ruining my bank holiday weekend , ring main IR readings as...
Replies
3
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Long shot but thought I’d try, have a lighting circuit that trips the RCD as soon as the neutral touches the neutral bar for said RCD. Bypass that...
Replies
6
Views
2K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K
1pm, quite happy doing my planned job. Builder then asks if I could go out to another job where the top lights have all tripped out. I like peace...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock