Can anybody assist me with the conflict between Napit codebreakers and the 18th Regulations please.
I have just had an EICR done on a purpose built flat built in 2006 (conforming to the 16th Regulations), the electrician states that according to the 18th edition I don't need RCD protection for all circuits but because he is using Napit Codebreakers his EICR preforms effectively self populates with a C2. This means he will have to relocate a timer to another enclosure, fit RCD protection etc etc all in around £600. I either pay for the work to be done or no satisfactory EICR. Just to add there are another 150 flats in the building and there are no special alterations or similar the would give rise to any suspicion of any danger. I rang Napit and they no longer speak to members of the public and I'm told codebreakers is a subscription only document .....so it looks like it's a pay up and smile !!!! Any thoughts anyone ?
I have just had an EICR done on a purpose built flat built in 2006 (conforming to the 16th Regulations), the electrician states that according to the 18th edition I don't need RCD protection for all circuits but because he is using Napit Codebreakers his EICR preforms effectively self populates with a C2. This means he will have to relocate a timer to another enclosure, fit RCD protection etc etc all in around £600. I either pay for the work to be done or no satisfactory EICR. Just to add there are another 150 flats in the building and there are no special alterations or similar the would give rise to any suspicion of any danger. I rang Napit and they no longer speak to members of the public and I'm told codebreakers is a subscription only document .....so it looks like it's a pay up and smile !!!! Any thoughts anyone ?