I posted this on a different forum but didn't get a lot of discussion so resharing this here for more feedback.


My friend bought a 10kw Comfort Zone Electric Heater

(see: https://www.amazon.com/Comfort-Zone...er+cz269er+10000+watts&qid=1615526178&sr=8-13)

And I'm trying to figure out conductor size and overcurrent protection for him.

With Ohms law I get 10kw at 240v = load size of 41.67 amps.

According to NEC Article 424 Fixed Electric Space Heating Equipment, this ceiling mounted electric heater is a continuous load. And must be multiplied 125 % of the load = 52.0875 amps. I emailed the manufacturer what amps the blow motor is rated at but haven't gotten a response yet. Regardless - 6/2 Romex is rated at 55 amps and the next closest Overcurrent Protection Device (Curcuit Breaker and separate Disconnect) would then theoretically be at 60 amps.

I read the manual and it doesn't mention continuous loads (seems to ignor it completely). Can't figure out how to upload pictures of manual but it only say that the device is at 10kw, 240V 69 Hz, Phase1, 41.67 amps and BTU/Hour: 32, 122. Wire should.be copper at a rating of 75C, fuse size 50amps and min copper wire size at: 6AWG.

So which Breaker Size should I side with? The 50 amp according to the manual or should I use a 60 amp breaker as I calculated via the NEC?


I am also wondering if 4-2 Romex (6-2 Romex would be awesome if allowable) would be cheaper than running #6 THHN b/c of need for an EMT raceway.

Thanks for the help!
 
according to our regs here, Ib<In<Iz, where Ib is the actual load current. In is the breaker rating, Iz is the max. current for the selected cable. so in your case, 41.67A Load)< 50A (breaker rating) < 55A (6/2 Romex max, current). so that would comply.
 
I posted this on a different forum but didn't get a lot of discussion so resharing this here for more feedback.


My friend bought a 10kw Comfort Zone Electric Heater

(see: https://www.amazon.com/Comfort-Zone...er+cz269er+10000+watts&qid=1615526178&sr=8-13)

And I'm trying to figure out conductor size and overcurrent protection for him.

With Ohms law I get 10kw at 240v = load size of 41.67 amps.

According to NEC Article 424 Fixed Electric Space Heating Equipment, this ceiling mounted electric heater is a continuous load. And must be multiplied 125 % of the load = 52.0875 amps. I emailed the manufacturer what amps the blow motor is rated at but haven't gotten a response yet. Regardless - 6/2 Romex is rated at 55 amps and the next closest Overcurrent Protection Device (Curcuit Breaker and separate Disconnect) would then theoretically be at 60 amps.

I read the manual and it doesn't mention continuous loads (seems to ignor it completely). Can't figure out how to upload pictures of manual but it only say that the device is at 10kw, 240V 69 Hz, Phase1, 41.67 amps and BTU/Hour: 32, 122. Wire should.be copper at a rating of 75C, fuse size 50amps and min copper wire size at: 6AWG.

So which Breaker Size should I side with? The 50 amp according to the manual or should I use a 60 amp breaker as I calculated via the NEC?


I am also wondering if 4-2 Romex (6-2 Romex would be awesome if allowable) would be cheaper than running #6 THHN b/c of need for an EMT raceway.

Thanks for the help!
My friend all you need is cable rated for 60 amps and install a 60 amp double pole breaker. They have wire at Lowe’s or Home Depot that will be good for 60 amps. Good luck
 

Reply to NEC or Product Manual? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I would like to ask advice on a breaker size. Back in 2001 I turned my garage into a woodworking shop with several 240v machines. To power them I...
Replies
2
Views
1K
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
1
Views
701
Hi folks. I'm asking so that I can do some planning, and then hire a local electrician to do the work. WHAT: This is my first question, ever...
Replies
3
Views
1K
Hi, I just wired a garage electric car charger (EVSE). The EVSE is configured for pulling 32 amp (240V) maximum, and directly connected. I am...
Replies
7
Views
2K
Ok, I've got an issue I can't figure out to save my life. Background: I'm putting in a 100a sub panel in my detached 2 car high bay garage...
Replies
1
Views
823

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock