Discuss need for a fused switch for boiler / and boiler earth cross bonding in the UK Electrical Forum area at ElectriciansForums.net

NickTG

DIY
Reaction score
5
hi there
as i write this i realise i have 3 interconnected questions about fused switches; two relating to my boiler (hope its not to cheeky to ask 3 questions all in one go :) )

Question1:
i have a radial circuit 1.5mm cable on a 6amp fuse from my consumer unit straight to the boiler where it is wired direct to the boiler (the circuit does not service any other appliance). Do i need an intermediary fused switch (or are fused switches needed when the appliances being serviced is not in itself a fused appliance or on a smaller cable to its supply feed?)

Question 2:
on my oven circuit it used to have a normal 2 gang switched socket at the back of the oven and i had 2 fused plugs one for the oven (just normal 60cm oven in kitchen units) and one for the gas hob (electric for ignition). About 7 years ago when i had a new hob, the gas guy said i should not have switches as it can create a spark so both the oven and the hob were hard wired into the socket - but there is no fuse switch. Ive recently bought a new oven 2.8kw and i now see it comes with a normal plug ! - am i right in thinking there is no longer any need to hard wire these alliances in and a socket with a plug is ok ?

Question3
Ive also taken the bottom cover off of the boiler and taken a pic of the bonding - there is a 16mm cable coming into the boiler and from that there is 6mm cable spanning across the 5 pipes is this what is commonly referred to as cross bonding to boiler ? (it looks like somewhere along the way ive lost a couple of tags which i should replace)
 

Attachments

  • WhatsApp Image 2022-05-27 at 4.10.01 PM.jpeg
    324 KB · Views: 30
hi there
as i write this i realise i have 3 interconnected questions about fused switches; two relating to my boiler (hope its not to cheeky to ask 3 questions all in one go :) )

Question1:
i have a radial circuit 1.5mm cable on a 6amp fuse from my consumer unit straight to the boiler where it is wired direct to the boiler (the circuit does not service any other appliance). Do i need an intermediary fused switch (or are fused switches needed when the appliances being serviced is not in itself a fused appliance or on a smaller cable to its supply feed?)
You probably don't need the fuse, though it is best to check what the boiler manufacturer specifies.

However, it is very off not to have a local means of isolation to allow safe servicing of the boiler. So the short answer is there should be a switch, and probably making that a FCU is as good as anything.
Question 2:
on my oven circuit it used to have a normal 2 gang switched socket at the back of the oven and i had 2 fused plugs one for the oven (just normal 60cm oven in kitchen units) and one for the gas hob (electric for ignition). About 7 years ago when i had a new hob, the gas guy said i should not have switches as it can create a spark so both the oven and the hob were hard wired into the socket - but there is no fuse switch. Ive recently bought a new oven 2.8kw and i now see it comes with a normal plug ! - am i right in thinking there is no longer any need to hard wire these alliances in and a socket with a plug is ok ?
A photo is needed here. If it is a typical 32A ring final circuit then any equipment off it should be fused, so either a 13A plug & socket, a FCU, or just the fuse (FCU without switch). But again no local means of isolation is very bad practice and in some case (e.g. Scottish building regulations) it is a requierment for accessible isolation for kitchen appliances & white goods.
Question3
Ive also taken the bottom cover off of the boiler and taken a pic of the bonding - there is a 16mm cable coming into the boiler and from that there is 6mm cable spanning across the 5 pipes is this what is commonly referred to as cross bonding to boiler ? (it looks like somewhere along the way ive lost a couple of tags which i should replace)
The big cable could be 10mm or 16mm and should be to the main earth terminal. The regulations normally specify this as close to the entry point after the gas meter as practical and before and T-branches, so it is possible this was deemed the easiest place to bond it.

The other bonding is typically done, though with a metal boiler somewhat superfluous!

However, the way the T&E cable is joined it no (presumably) supply the boiler on the left is appalling! No cable support and no box covering the terminals.
 
You probably don't need the fuse, though it is best to check what the boiler manufacturer specifies.

However, it is very off not to have a local means of isolation to allow safe servicing of the boiler. So the short answer is there should be a switch, and probably making that a FCU is as good as anything.

A photo is needed here. If it is a typical 32A ring final circuit then any equipment off it should be fused, so either a 13A plug & socket, a FCU, or just the fuse (FCU without switch). But again no local means of isolation is very bad practice and in some case (e.g. Scottish building regulations) it is a requierment for accessible isolation for kitchen appliances & white goods.

The big cable could be 10mm or 16mm and should be to the main earth terminal. The regulations normally specify this as close to the entry point after the gas meter as practical and before and T-branches, so it is possible this was deemed the easiest place to bond it.

The other bonding is typically done, though with a metal boiler somewhat superfluous!

However, the way the T&E cable is joined it no (presumably) supply the boiler on the left is appalling! No cable support and no box covering the terminals.
thanks for cover all the points PC1966 - comments really appreciated and very clear - thanks :)
 
You probably don't need the fuse, though it is best to check what the boiler manufacturer specifies.

However, it is very off not to have a local means of isolation to allow safe servicing of the boiler. So the short answer is there should be a switch, and probably making that a FCU is as good as anything.

A photo is needed here. If it is a typical 32A ring final circuit then any equipment off it should be fused, so either a 13A plug & socket, a FCU, or just the fuse (FCU without switch). But again no local means of isolation is very bad practice and in some case (e.g. Scottish building regulations) it is a requierment for accessible isolation for kitchen appliances & white goods.

The big cable could be 10mm or 16mm and should be to the main earth terminal. The regulations normally specify this as close to the entry point after the gas meter as practical and before and T-branches, so it is possible this was deemed the easiest place to bond it.

The other bonding is typically done, though with a metal boiler somewhat superfluous!

However, the way the T&E cable is joined it no (presumably) supply the boiler on the left is appalling! No cable support and no box covering the terminals.
You probably don't need the fuse, though it is best to check what the boiler manufacturer specifies.

However, it is very off not to have a local means of isolation to allow safe servicing of the boiler. So the short answer is there should be a switch, and probably making that a FCU is as good as anything.

A photo is needed here. If it is a typical 32A ring final circuit then any equipment off it should be fused, so either a 13A plug & socket, a FCU, or just the fuse (FCU without switch). But again no local means of isolation is very bad practice and in some case (e.g. Scottish building regulations) it is a requierment for accessible isolation for kitchen appliances & white goods.

The big cable could be 10mm or 16mm and should be to the main earth terminal. The regulations normally specify this as close to the entry point after the gas meter as practical and before and T-branches, so it is possible this was deemed the easiest place to bond it.

The other bonding is typically done, though with a metal boiler somewhat superfluous!

However, the way the T&E cable is joined it no (presumably) supply the boiler on the left is appalling! No cable support and no box covering the terminals.
thanks for cover all the points PC1966 - comments really appreciated and very clear - thanks :)
 

Reply to need for a fused switch for boiler / and boiler earth cross bonding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'd like to move the existing socket that feeds the boiler down to where I've pencilled in that can be seen on the photo. The socket to the...
Replies
10
Views
841
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
645
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
736
Hi, My current oven is hardwired to a fused connection plate with a 13Amp fuse inside and power switch. That is then connected to the MCB labelled...
Replies
1
Views
884

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock