Can some one please help with this. I am getting 11v on two light circuits, it should be 240v Other lights in the circuit are working OK, it is just the hallway light and bedroom light that do not work. I have opened up the two switches and batten holders to check for loose wires but everything looks OK. So why would the circuit only have 11v on it? I assume it is a loose wire some where, are I correct?
 
What are you using to meet sure the 11v and what are you measuring between?

Hobby type multimeters are not calibrated and could give false readings when measuring.

If lights are not working, then check bulbs, check connections, check other recent work hasn’t drilled through a cable.
 
using a $200 multimeter, I have removed 2 batten holders (light fitting) and 2 light switches and there are no loose wires. Bulbs are OK but will not work on 11v, as they are rated 240v. I am getting 11v at the batten holder and switches. Owner said lights started flickering then went dead.
 
junction box above ceiling? a terminal in a batten or a switch witth screw clamping insulation? a conductor broke right in the terminal so you can't see it, but a tug would find it?also, measure volts Line - E, if thet reads 240V, then you have a broken neutral
 
using a $200 multimeter, I have removed 2 batten holders (light fitting) and 2 light switches and there are no loose wires. Bulbs are OK but will not work on 11v, as they are rated 240v. I am getting 11v at the batten holder and switches. Owner said lights started flickering then went dead.
Yes but where are you measuring from to get 11v? L/N L/N etc
 
My guess would be no Neutral, break out the wander lead and do an rN from the board to the fittings.
Edited to add, with my equipment I'd check voltage L-E and L-N to confirm this, 240V L-E would strongly indicate a lost Neutral.

If, as suspected you have an open circuit, you need to start looking back along the circuit checking rN until you have continuity.

Your fault will be between here and the faulty fitting.

Have any lights/switches been altered in other rooms?
 

Reply to Need help finding fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening all, I had a quick Friday afternoon domestic job that has turned into a PITA and I'd appreciate your help. While adding some new lights...
Replies
10
Views
857
Hi All, Would be grateful for some advice. Would like to add an additional light (Undercabinet 8W LED Batten light) to a two-way light switch...
Replies
7
Views
613
Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
I disassembled a Christmas light projector to try and identify the cause of why the images from the projector weren't moving at all, when they...
Replies
27
Views
857
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock