Search the forum,

Discuss Need some ideas - RCD tripping but everything tests fine.... in the UK Electrical Forum area at ElectriciansForums.net

RCBOs with a solid neutral are far from ideal with any earthing system.
If there is a neutral to earth fault then the rcbo will react by disconnecting the line and not actually disconnect the fault.
Thus it appears to the user that a fault has occurred but it is now disconnected because the protective device has operated, when in actual fact the fault is still there.
Plus of course you now have a portion of the neutral current from the entire installation diverting through the fault.

Additionally manufacturers have their own requirements for maximum Zs for correct operation of their single pole RCBOs, which may not be achieveable on a TT system.

The point that springs to mind here is that a N-E fault on a system with no RCD element will remain undetected with the same risk of neutral current diverting down the parallel path caused by the fault, at least with a SP RCBO the user will have an indication that there is a problem. I've not come across any manufacturers who give their own max Zs values for standard RCBO's, can you give an example of this?
 
The point that springs to mind here is that a N-E fault on a system with no RCD element will remain undetected with the same risk of neutral current diverting down the parallel path caused by the fault, at least with a SP RCBO the user will have an indication that there is a problem. I've not come across any manufacturers who give their own max Zs values for standard RCBO's, can you give an example of this?

yes a circuit without RCD protection won't have any means of detecting a N-E fault, however what it does do is disconnect all of the faults it is designed to detect and is capable of protecting against.
The rcbo does not disconnect all of the faults which it is designed to detect or protect against.

The first one that springs to mind is the little company known as Schneider, particularly the part of it formerly known as Merlin Gerin.
 
TBH if I have these sort of problems with a single RCD install I don't waste a great deal of time if IR tests with everything connected are good. Advise to change to RCBO's. Whatever you do nuisance tripping is almost inevitable with such an install, even if you find a problem chances are something else will trip it before long and then you'll be back again for SFA because "I've already paid you once to fix it". A single RCD don't comply any more anyway!
why does a single rcd not comply
 
I know I've read somewhere about SP RCBO's not being suitable for TT systems but cant remember where and am still sceptical. In fact on our last NICEIC visit I asked the question and got a blank look.
If anyone can shed any light......
On Site Guide page 20, then 32, 33 and 34.
Says:
Full RCBO CU with main switch suitable for TN and TT.
Twin RCD CU with main switch only suitable for TN
Twin RCD CU with 100mA time delayed RCD suitable for TN and TT.

Many other configurations are also talked about.
 
No, it's tripping at 19mA on ramp test with everything on. (23mA disconnected). So there is nornally 4mA leakage.
I realise 8M is a bit low....
Think I'm gonna invest in a leakage clamp meter and have a deeper look - if I get called back that is - still no tripping 48 hrs on......

I tried what you are doing, but I ramp tested a tripping RCD at 19mA with all circuits on, then again at 19mA with all circuits off. Then I purchased a leakage clamp meter and found the leakage is 19mA with all circuits turned on. And soon identified the kitchen ring as the biggest leakage of 10.5mA.
 
I tried what you are doing, but I ramp tested a tripping RCD at 19mA with all circuits on, then again at 19mA with all circuits off. Then I purchased a leakage clamp meter and found the leakage is 19mA with all circuits turned on. And soon identified the kitchen ring as the biggest leakage of 10.5mA.

Ouch... so its almost certainly accumulated leakage causing the tripping.

You'll find the earth leakage meter VERY handy

and 10/10 for your feedback ..... so many people don't!
 
No Murdoch, this guy is not the OP , I am!!!!
I haven't fed back yet because I haven't had to go back to the job yet, it's still not tripped since I swapped the RCD (and I still haven't got round to buying me earth leakage tester yet...)
So it's looking more like a faulty RCD now.... (as unlikely as that seems).
I won't sing too loudly yet as I think it will trip again......
 

Reply to Need some ideas - RCD tripping but everything tests fine.... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
875
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
944
Hello - hope someone can advise please. I have a recently purchased second hand Myford lathe which has a 3-phase inverter (Siemens Micromaster...
Replies
11
Views
1K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock