Hi guys

i need an idiots guide to the following and i know you guys know your stuff

swa armouring as a cpc only

now i think i know the following , but how to put it altogether and where 8.8 comes from is just confusing me , so if i start again and you good people

so
4 core 35mm swa has csa of 78mm
and swa for a cpc needs to be at least 46 to be adequate

as per attachments

how do i actually find out the actual copper equivalent of the swa so i can say 35mm swa = 9.2mm earth

really need to understand this as seems to be cropping up on a weekly basis
and the more i read the more confused im getting lol

thanks guys
Screen Shot 2017-12-06 at 19.49.03.png
Screen Shot 2017-12-06 at 19.49.24.png
Screen Shot 2017-12-06 at 19.49.03.png
 
Last edited:
Guidance note 8 suggests a figure of 8.5 copper equivalent ratio to steel and 1.68 for aluminium to copper ratio.
So if you had 85mm steel then 85/8.5= 10mm copper equivalent.
35mm steel divide by 8.5 would be 4.11mm copper
 
Is it doing the calculation or reading/interpretation of the table you are having a problem with?
Using your example, a 35mm, 4 core SWA has swa copper equivalent of 37.2mm2 or 25mm2 if xple - taken from the table.
Agree Polo, not sure but it may be the OP is trying to find out the csa of the cpc for the cable he is specifying i, e, for example is the tabulated CU size is suitable for the 35mm2 he is speaking of, mind you that's how I look at it I may be wrong, but not disputing your answer.
 
so 35mm 4 core swa with steel at 78mm / 8.5 = 9.17mm copper conductor
Yeah really if your considering using the steel armour as a protective bonding conductor at domestic level then to comply with the minimum CSA of 10mm copper conductors needed then 85mm is the minimum steel CSA you can use of copper equivalent
 
That table is a at best a rough guide, and at worst just plain wrong.

There isn’t a direct ‘copper equivalent’ for use as a CPC as there is more to the calculation than just comparing conductivity.
The simple answer is to use the equations given in BS7671 to calculate it as and when required, either the adiabatic equation or the simplified method. Actual steel CSA of the armour should be in the manufacturers data for the cable you are using.

If you are considering the steel armour for use as a bonding conductor then it can be simplified to equivalent conductivity. Steel has roughly 9 times less conductivity than copper, so you can multiply the required copper csa by 9 to get the required steel csa. Using this method for a cpc would result in a ridiculously oversized steel csa!
 

Reply to need to fully understand ... and im just not getting it in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, Im quoting to install an EV charger (Dont worry - fully registered, but only been 2 weeks so i'm still picking bits up). Consumer unit...
Replies
1
Views
1K
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
NICEIC Certification Scheme Getting accredited to
Looking for some advice regarding joining a CPS. I've been in the electrical industry in various roles for nearly 10 years. I started my...
Replies
15
Views
1K
Hi Guys/Girls A quick question. Would I need to TT a stand alone socket detached from main building (TNCS) that could be used with a Class I...
Replies
3
Views
1K
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
488

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock