Neutral lead on RCBO'S

Discuss Neutral lead on RCBO'S in the UK Electrical Forum area at ElectriciansForums.net

K

Kev2632

What exactly are the neutral leads for? and if a neutral to earth happened on a board with just RCBO'S in it, why doesnt the fault travel along that neutral and affect the other RCBO's?
 
As far as I understand it, if there is an N/E fault on RCBO1 and RCBO2 shares a neutral on the load side then RCBO2 will also see an Earth fault and so it will trip.
Correct.

A borrowed neutral N-E fault will trip both because both neutrals (or shared one) will be connected to earth.


Just to point out that single-module RCBOs are only single-pole switches.
 
So when the rcbos are single pole devices then, what would in the scenarios we have described with the borrowed neutral case, and the borrowed neutral with the N-E fault on Rcbo 1? What happen in both of these scenarios?? :/
 
No. It's not isolated.

So, if borrowed or connected to another neutral it will divert current from the second RCBO.

If there is an N - E fault it will be on both RCBOs.
 
Last edited by a moderator:

So just to clear this up for the single pole RCBO, in relation to the drawing on page 3- bearing in mind they are single pole RCBO's instead, when we have just a borrowed neutral on RCBO 1 & 2, It will trip both RCBO, when RCBO 1 trips the current will go down through RCBO 1 neutral cable, through the RCBO1 neutral lead and trip RCBO 2 as well yea?? and when we have the borrowed Neutral and neutral to earth fault on RCBO1 it will trip RCBO1 and will it no affect all the other RCBO's as well now??? as the neutral is not isolated from the rest of them??
 
So just to clear this up for the single pole RCBO, in relation to the drawing on page 3- bearing in mind they are single pole RCBO's instead, when we have just a borrowed neutral on RCBO 1 & 2, It will trip both RCBO,
Yes, because the current is going out through one RCBO and (some of it) back through another - so imbalance.

when RCBO 1 trips the current will go down through RCBO 1 neutral cable, through the RCBO1 neutral lead and trip RCBO 2 as well yea??
Yes, probably at the same time if lamps on both circuits turned on.
It's easier to see if you draw the circuit and follow the current path(s).

and when we have the borrowed Neutral and neutral to earth fault on RCBO1 it will trip RCBO1 and will it no affect all the other RCBO's as well now??? as the neutral is not isolated from the rest of them??
Not sure if you meant now or not.

Don't forget that an N-E fault will only trip the RCBO whose neutral has faulted to earth and the one whose neutral is connected to the neutral of the first - not any others because the fault is on the load side and load side neutrals are not connected (except in these fault conditions).
 
Yes, probably at the same time if lamps on both circuits turned on.
It's easier to see if you draw the circuit and follow the current path(s).

So the current wont travel back up the supply side of an rcbo then?

Not sure if you meant now or not.

Don't forget that an N-E fault will only trip the RCBO whose neutral has faulted to earth and the one whose neutral is connected to the neutral of the first - not any others because the fault is on the load side and load side neutrals are not connected (except in these fault conditions).


Yea i meant now sorry, ahh right so once the RCBO 1 has tripped the fault is isolated from the rest of the circuits as the current wont get past the supply side of RCBO 1 yea??
 

Reply to Neutral lead on RCBO'S in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock