Discuss New here... and here is a an interesting DB I've come across... need some help with EICR for it! in the The Welcome Forum area at ElectriciansForums.net

I

itsonly3wires

Hello, I've got a question that I thought I throw out to the crowd and see what comes back... I am a little stuck with a recent EICR that followed a change of occupier.

The home is 30 ish years old and has been extended several times. It is a fairly large home with swimming pool, multiple outbuildings and annexes.

The main DB is where I am struggling a little.

The supply is single phase fed from two meters. It enters the DB via 25mm2 tails two from one meter. One from the other meter. At a glance it looks like a 3 phase supply... there is a 125A main switch to the DB and there is a single neutral. It is a three phase DC with colours marking out where you would normally expect to find L1, L2 and L3.

The issue I am having is that the single neutral is carrying the entire current from both supplies and so too is the meter it is connected to. One meter has no neutral connection to the DB.

The meter (I think) is rated to 80 amps... but the full load is passing through it.

The tails (meter to DB) are short so I am less concerned about the neutral being overloaded.
The main switch on the DB is rated 125A so should be fine but I imagine the rating is for a reasonably well balanced 3 load across all 3 phases. It isn't. No current is flowing between phases so everything must be going down neutral.

For clarity the main DB is the only source of distribution to the whole building. There are a further 5 sub DB's fed off this one board. The board is near full to capacity at 0.4 diversity.

So my question is this.... any harm in the neutral from one meter handling this load? What about the main switch? Are there any regs transgressions in this? I've never encountered this particular set-up before.

Here is the full horror:
IMG_3164.JPG
 
I think you'll find that the neutral connections on the meter are simply a big terminal block with a small connection for use by the voltage coil. The current coil which is connected in series with the two line terminals are what the rating applies to.
 
Are you sure there isn't 2 phases there? Cause that's what it looks like.

Also the main switch is rated at 125A per pole, it doesn't care if it's balanced load.
 
Yep - just a big terminal block for the neutral... but I assume the rating is still relevant. The insulation and terminal block are more than capable we can assume but it won't have been tested for this... therefore is it compliant?

@Rob - definitely not 2 phases. 240V across phase to neutral. 0V across "phases".

The 125A switch isn't a question of balance.... it is a question of how much is going through that neutral contact. If there is 65 Amps per "phase" then there is 130 Amps going via that single neutral pole.

In most 3 phase installations (for which this switch is intended) some current would be phase to phase and not 100% of the current via the neutral pole.

This installation is littered with C1's regardless of this little problem! Any other thoughts are most welcome... I really don't like the look of it. Most of the install is OK but I am not sure the use of the three phase CU was the best move. It would have been better if two CUs were installed each taking a supply from the meter. I'm sure that single neutral conductor taking the load of the three single phase conductors is less than optimal and I'm sure that neutral pole of the switch is over loaded.
 
Hello, I've got a question that I thought I throw out to the crowd and see what comes back... I am a little stuck with a recent EICR that followed a change of occupier.

The home is 30 ish years old and has been extended several times. It is a fairly large home with swimming pool, multiple outbuildings and annexes.

The main DB is where I am struggling a little.

The supply is single phase fed from two meters. It enters the DB via 25mm2 tails two from one meter. One from the other meter. At a glance it looks like a 3 phase supply... there is a 125A main switch to the DB and there is a single neutral. It is a three phase DC with colours marking out where you would normally expect to find L1, L2 and L3.

The issue I am having is that the single neutral is carrying the entire current from both supplies and so too is the meter it is connected to. One meter has no neutral connection to the DB.

The meter (I think) is rated to 80 amps... but the full load is passing through it.

The tails (meter to DB) are short so I am less concerned about the neutral being overloaded.
The main switch on the DB is rated 125A so should be fine but I imagine the rating is for a reasonably well balanced 3 load across all 3 phases. It isn't. No current is flowing between phases so everything must be going down neutral.

For clarity the main DB is the only source of distribution to the whole building. There are a further 5 sub DB's fed off this one board. The board is near full to capacity at 0.4 diversity.

So my question is this.... any harm in the neutral from one meter handling this load? What about the main switch? Are there any regs transgressions in this? I've never encountered this particular set-up before.

Here is the full horror:
View attachment 37631
3 phase DC?? Those meters are rated at 240 Volts
 
@Pete999 typo.... not sure if I was supposed to type 3 phase DB or CU... it just came out DC instead!

Here is what I meant...
It is a CU marked up for 3 phases with 4 pole isolation and feed arranged inside in the usual pattern of 3.

Someone has wired it up with 3 25mm2 tails all from the same phase.

That results in the neutral potentially being overloaded as it is carrying all the current and the phase conductors / main switch carry just a third each.

Since in an application where there is only a single phase all current flow phase to neutral. There is no phase to phase path (obviously).
 
From what I can see both meters are single phase, the right one appears to have two outgoing line conductors into one terminal. One neutral goes to the right meter which from where the board neutral is connected. The neutral for the left side meter goes direct to the service head, correct?
 
Thanks all...

The supply is not multi-phase. It is single phase. Proven via meter measuring 0 volts across line conductors. and 240V to neutral / earth.

One meter has two line conductor tails from it and a single neutral
The other meter has a single line conductor and no neutral

The sum of all breakers in the DB is 543A
At 0.4 diversity we have 217.2A

So there is possibly 217.2A on that neutral conductor which is broken by a 125A main switch.

The BS1361 DNO fuse will offer some protection since there are two meters and thus just two fuses in play... so we could say that we are limited to 200A in theory... but the reality is that a BS 1361 100A fuse is going to take an eternity to disconnect a 110A load.

Sorry for the poor photo!

What do you think? The whole DB is a C1 due to it failing to meet IP2X I might as well C1 it for having an undersized switch.
 
You do realise a C1 is immediate danger present?
And why have you added all the mcbs up?
It's the potential loading you need to apply diversity to not adding all the breakers
 
C1 for having a penetration that a whole hand can fit in. DB is in a cupboard used by the family including children for school bags, coats and shoes.

If you look closely at the photo the tails are not nicely dressed and bare copper is visible in the line conductors on the DB side of the meters. The cover that should be over that is broken and again that wouldn't meet IP2X... although I'm not sure it has to but in this instance is absolutely must given it is a very real possibility that a metal zipper, bag buckle or wet coat could quite likely come into contact with it.

The install is not very nice in general. There are 4 circuits that are a mess. It fails to meet Zs to a DB. There is evidence of rodent damage to some cables, the swimming pool lights are full of water, there is thermal damage to a FCU, there is cable trucking missing for swimming pool plant room... I have something like 4 C1 and 12 C2/C3 out of 27 circuits.
 
@Ian1981 swimming pool pumps, sauna, spa air pump are high demand (for a residential install) and they are normally in use simultaneously. Then add in an electric hob, and oven and we are starting to pull close to 80amps.
The home has a second kitchen, external workshop with a large inverter. I'm being lazy... with my methodology... sum the breakers, multiply by 30% perhaps... here I thought 40%... but there is easily a 100 amp demand on this place. Peak it will exceed it and there is a very real chance that it is well north of 125A.
 
@Ian1981 swimming pool pumps, sauna, spa air pump are high demand (for a residential install) and they are normally in use simultaneously. Then add in an electric hob, and oven and we are starting to pull close to 80amps.
The home has a second kitchen, external workshop with a large inverter. I'm being lazy... with my methodology... sum the breakers, multiply by 30% perhaps... here I thought 40%... but there is easily a 100 amp demand on this place. Peak it will exceed it and there is a very real chance that it is well north of 125A.
 

Reply to New here... and here is a an interesting DB I've come across... need some help with EICR for it! in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
644
Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Replies
4
Views
427
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
740
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
870
I didn't get a picture so will have to wait until I go back again but I've done a crude drawing of what was there. Its in a commercial set up...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock