I also agree with the opinion , that there is nothing wrong with fitting Dual RCD DB. It's mainly matter of convenience for me, when using RCBO's instead of dual RCD, in case of a fault. At the moment we are finishing residential apartments complex, using exactly the same Hagger DB's. I must have tested 300 of them so far. Regarding the mentioned above DB job, it's cheaply done, but this very common, when a client choses the cheapest offers. Normally, I would use gland for the meter tails and supporting clips. Cables contained in 50x50mm trunking(or bigger) , and using metal bushes/lockrings instead of the knockouts. All gaps/cable entry sealed with fire mastic. And at the end - all connections within DB tightened with torque screwdriver by manufacturer's specifications(nearly nobody is doing that, but yesterday was called out to sort a problem because of loose busbar connection in DB). Also I would leave a spare MCB before the 1st RCD(for security alarm/fire alarm/ disability / garrage DB circuits).
There are many things in the OP's board that a lot of electricians would do differently, but I tried to limit criticism to issues that breached actual regulations and avoid stating what might be considered best practice.