Search the forum,

Discuss New rewire and fuse board - views on work. in the UK Electrical Forum area at ElectriciansForums.net

I also agree with the opinion , that there is nothing wrong with fitting Dual RCD DB. It's mainly matter of convenience for me, when using RCBO's instead of dual RCD, in case of a fault. At the moment we are finishing residential apartments complex, using exactly the same Hagger DB's. I must have tested 300 of them so far. Regarding the mentioned above DB job, it's cheaply done, but this very common, when a client choses the cheapest offers. Normally, I would use gland for the meter tails and supporting clips. Cables contained in 50x50mm trunking(or bigger) , and using metal bushes/lockrings instead of the knockouts. All gaps/cable entry sealed with fire mastic. And at the end - all connections within DB tightened with torque screwdriver by manufacturer's specifications(nearly nobody is doing that, but yesterday was called out to sort a problem because of loose busbar connection in DB). Also I would leave a spare MCB before the 1st RCD(for security alarm/fire alarm/ disability / garrage DB circuits).

There are many things in the OP's board that a lot of electricians would do differently, but I tried to limit criticism to issues that breached actual regulations and avoid stating what might be considered best practice.
 
Hi guys I’ve included more pics including that of the SPD. (In my non electrical brain it shows an earth coming out from the top of the SPD but there there are the two bit coming out. As I said when we opened the box I never saw an earth wire in the box nor connected to the SPD.
This is the same as the one I fitted. I think it connects to earth via the steel enclosure and din rail, but I have emailed hager for clarification and will update when I have news
 
This is the same as the one I fitted. I think it connects to earth via the steel enclosure and din rail, but I have emailed hager for clarification and will update when I have news
Hi well like you I had no cpc cable in the box or coming out of it, and from your pic mine looks the same if that is of any help.

Looking into RCBO’s now - is there any reason why the Hager enclosure couldn’t be used ?
This is the exact one Design 10 - 14 Way 100A Dual Split Consumer Unit c/w 2 RCDs (Type A) + SPD | Hager (VML914CUSPD) - https://www.tlc-direct.co.uk/Products/HGVML914CUSPD.html
 
There are many things in the OP's board that a lot of electricians would do differently, but I tried to limit criticism to issues that breached actual regulations and avoid stating what might be considered best practice.
Hi, could you please tell me best practice ?

I’ve seen that people install a 100 amp isolator before the board.

Forgive me I don’t want to be rude to anyone, but is it possible he passed after doing one of these short courses, like the 3 week ones, rather than an apprenticeship / or the normal way of college/ training etc.
 
Hi, could you please tell me best practice ?

The post I was responding to mentioned several ways in which they'd have approached this board differently and I'd have taken a similar approach, but not doing so isn't a breach of any regulation.

Containment of cables would give a more aesthetically pleasing look to the installation, but sheathed cables such as the twin and earth used in domestic installations does not need to be contained.

The issues to which you can legitimately raise objections have already been covered: Power and lighting should be split across both RCDs, so loosing one bank of circuits will ensure either power or light remains in any given area of the home. Cables (including incoming tails) should be suitably supported and restrained - there are many ways in which this can be done, including the simple cable clip. If there is sufficient space for finger access where tails come in the bottom, then this should be filled. Cables should be protected from metal edges as they come into the board, which can be remedied through the use of grommet strip.

I know not all issues will be covered in the above paragraph, as I'm working from memory of what I read last night, but am trying to draw a clear distinction between how electricians might approach this job and what is actually required from a regulatory perspective.


Edit: An isolator after the meter is very helpful for future work or maintenance, but no regulation mandates this additional means of isolation.

As for training? I couldn't comment - many time served electricians turn out shoddy work and there are also electricians who came to the industry through a short course and go on to turn out exemplary work. Knowledge is very useful, but can be renered pointless if not accompanied by a good work ethic.
 
Last edited:
So my research seems to indicate that RCBO's can fit within the board. They are listed as an accessory by TLC.

The board code brings up that is High Intensity - how many RCBO's I can fit, I don't know. A single RCBO from TLC is nearly £30 on its own.
Should I get an electrician to change everything to RCBO (if possible). If not should I get sockets and lights on their own RCBO, (the kitchen is on its own board, so if the new board trips I still have light and power downstairs).

I'm also getting a car charger, and solar, I assume these are both high risk items. So I should spend the extra and also put them on a RCBO on the main Hager Board ?

Or should I spend even more, and get the car charger, and solar, on its own RCBO board, with surge ?
 
So my research seems to indicate that RCBO's can fit within the board. They are listed as an accessory by TLC.

The board code brings up that is High Intensity - how many RCBO's I can fit, I don't know. A single RCBO from TLC is nearly £30 on its own.
Should I get an electrician to change everything to RCBO (if possible). If not should I get sockets and lights on their own RCBO, (the kitchen is on its own board, so if the new board trips I still have light and power downstairs).

I'm also getting a car charger, and solar, I assume these are both high risk items. So I should spend the extra and also put them on a RCBO on the main Hager Board ?

Or should I spend even more, and get the car charger, and solar, on its own RCBO board, with surge ?
The best thing to do is get another sparky in (A decent one) and let them plan it for you.

You certainly don't need all those circuits on separate rcbos.
 
The best thing to do is get another sparky in (A decent one) and let them plan it for you.

You certainly don't need all those circuits on separate rcbos.

Also unlikely to gain any benefit from the additional expense of changing to RCBOs and sourcing new busbar. I'd be inclined to leave the current set up in place, unless cumulative earth leakage happens to cause nuisance tripping (of which there have been no reports so far).
 
So my research seems to indicate that RCBO's can fit within the board. They are listed as an accessory by TLC.

The board code brings up that is High Intensity - how many RCBO's I can fit, I don't know. A single RCBO from TLC is nearly £30 on its own.
Should I get an electrician to change everything to RCBO (if possible). If not should I get sockets and lights on their own RCBO, (the kitchen is on its own board, so if the new board trips I still have light and power downstairs).

I'm also getting a car charger, and solar, I assume these are both high risk items. So I should spend the extra and also put them on a RCBO on the main Hager Board ?

Or should I spend even more, and get the car charger, and solar, on its own RCBO board, with surge ?

Even pairing down the number of circuits, you're looking at £300+ additional expenditure and for what gain?

EV charge point may present an issue with current installation, but there are a number of ways in which that issue could be overcome.

I'm not telling you not to make this change, but asking you to consider whether or not it's worth spending money on. One benefit would be that any fault to earth causes tripping of a single circuit, but is that really essential to you?
 
New posts

Reply to New rewire and fuse board - views on work. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
908
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
I'm getting an old fuse board upgraded in an office block. The electrician has just told me that most of the circuits don't have earth cables...
Replies
44
Views
4K
Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock