installing new shower just shower unit no new wiring involved , old house no rcd protection , i need to install an rcd for new shower correct?
 
Unless you can run surface / mechanically protect etc, then you do buddy. You can get shower RCD units fairly cheap though to be honest.
 
I suspect that the new shower unit will come with maker's instructions. They may mandate the use of an RCD.

Personally I would want an RCD at any place where water, electricity and people come together.
 
I had a shower job last week, customer bought 9.5 kW triton cheap, I turn up , no rcd protection, 6mm feed to shower. Looked at manual and they state must be on 30 ma rcd. So got her to change shower to 7.5 kW and I will plop a shower rcd unit next to board. Bindings all in place jobs a good un.
 
what's wrong with 9.5kW on 6mm 40A as long as it's ref. method C?
 

Reply to new shower in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just been called out to another burning shower switch.Upon removal the wires had been burnt and chared.One thing I've noticed on all burnt...
Replies
27
Views
1K
  • Locked
My house was built in the 1930s, The fuse in my service cut out is 60Amp and the wire coming from the street has a 16mm2 copper core(easy to see...
Replies
12
Views
612
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
761
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock