What are these occasions then?
Spin, that is incorrect.The EAWR does not apply to a domestic installation.
I have a vague memory of a reg somewhere that stated it should be earthed at at least one end and 'preferably' the supply end.
It should a earthed or connected to the same earthing system as used by the protective device protecting the SWA.
If the SWA was feeding a separated TT installation then clearly the conductive part of the SWA would be earthed from the supply (TN) end,and electrically separated from the earthing arrangement at the load end..Does this statement suggest that it can be connected to whatever earthing arrangement exists at the origin OR alternatively, connected to a separate earthing arrangement at the load end?
As you have disagreed Murdoch, and you will not accept that you are wrong.
Please read these quotes, verbatim, straight from the LAW of the land.
EAWR89 & HASAWA74.
EAWR89:
Persons on whom duties are imposed by these Regulations
3.—(1) Except where otherwise expressly provided in these Regulations, it shall be the duty ofevery–
(a)
employer and self-employed person to comply with the provisions of these Regulations inso far as they relate to matters which are within his control; and
(b)
manager of a mine or quarry (within in either case the meaning of section 180 of the Minesand Quarries Act 1954(2)) to ensure that all requirements or prohibitions imposed by orunder these Regulations are complied with in so far as they relate to the mine or quarry orpart of a quarry of which he is the manager and to matters which are within his control.
(2) It shall be the duty of every employee while at work–
(a)
to co-operate with his employer so far as is necessary to enable any duty placed on thatemployer by the provisions of these Regulations to be complied with; and
(b)
to comply with the provisions of these Regulations in so far as they relate to matters which are within his control.
HASAWA74:
3 General duties of employers and self-employed to persons other than their employees.
(1) It shall be the duty of every employer to conduct his undertaking in such a way as to ensure, so far as is reasonably practicable, that persons not in his employment who may be affected thereby are not thereby exposed to risks to their health or safety.
(2) It shall be the duty of every self-employed person who conducts an undertaking of a prescribed description to conduct the undertaking in such a way as to ensure, so far as is reasonably practicable, that he and other persons (not being his employees) who may be affected thereby are not thereby exposed to risks to their health or safety.
(2a) A description of undertaking included in regulations under subsection (2) may be framed by reference to—
the type of activities carried out by the undertaking, where those activities are carried out or any other feature of the undertaking;
whether persons who may be affected by the conduct of the undertaking, other than the self-employed person (or his employees), may thereby be exposed to risks to their health or safety.
(3) In such cases as may be prescribed, it shall be the duty of every employer and every self-employed person, in the prescribed circumstances and in the prescribed manner, to give to persons (not being his employees) who may be affected by the way in which he conducts his undertaking the prescribed information about such aspects of the way in which he conducts his undertaking as might affect their health or safety.
I did not say the EAWR does not apply to domestic work.Spin, that is incorrect.
Read the requirements of Reg 3, then look at HASAWA, Reg 3, and come back and tell me that EAWR does not apply to domestic work, and explain your defence against these laws.
It should be connected to the same earthing system as the protective device which protects the SWA cable is connected to.Does this statement suggest that it can be connected to whatever earthing arrangement exists at the origin OR alternatively, connected to a separate earthing arrangement at the load end?
It does though, if you, read, the law, the installation is under the control of the installer, thus the installation is under the control of the installer, ergo, EAWR applies.I did not say the EAWR does not apply to domestic work.
I said the EAWR does not apply to a domestic installation.
EAWR89:Ok this is all very well and could go on for weeks but please quote the exact wording of the exact regulation that clearly states armour must be earthed at the supply end.
Edit - reply to post #57.
If the SWA was feeding a separated TT installation then clearly the conductive part of the SWA would be earthed from the supply (TN) end,and electrically separated from the earthing arrangement at the load end..
So are you suggesting that the swa would need to be terminated in a separate enclosure before entering a metal consumer unit ( TT earthed) in an outbuilding for example?
No, the installation is under the control of the householder.It does though, if you, read, the law, the installation is under the control of the installer, thus the installation is under the control of the installer, ergo, EAWR applies.
You are missing the point the doing of the installation is under the control of the "electrician" no matter where they have been since or after, that job was under their control, they were at work, thus, EAWR & HASAWA applied at that time.No, the installation is under the control of the householder.
The installer bugged off ages ago and is probably installing other installations, or on here wondering where people get such weird ideas from.
It should be connected to the same earthing system as the protective device which protects the SWA cable is connected to.
It should not be connected to a separate earthing system.
You are missing the point the doing of the installation is under the control of the "electrician" no matter where they have been since or after, that job was under their control, they were at work, thus, EAWR & HASAWA applied at that time.
Employed or Self-Employed both apply.
Sorry you are getting confused about what it is the Regulations apply to.You are missing the point the doing of the installation is under the control of the "electrician" no matter where they have been since or after, that job was under their control, they were at work, thus, EAWR & HASAWA applied at that time.
Employed or Self-Employed both apply.
No, you are wrong, not me.Sorry you are getting confused about what it is the Regulations apply to.
To put it in simple terms, the ground does not have to comply with HASAWA.
If a worker then digs a hole in the ground, that task must comply with HASAWA.
Electricity does not have to comply with the EAWR.
How you use electricity when conducting a task for work must comply with the EAWR.
An installation in a building which is not used for work purposes does not have to comply with the EAWR.
How you use the electricity provided by that installation when conducting a task for work must comply with the EAWR.
An installation in a building that is a place of work, must comply with the EAWR.
How you use the electricity (irrespective of whether it is for a task of work) provided by the installation, must also comply with the EAWR.
Compliance with the EAWR can in many respects be achieved by compliance with BS7671.
So if this is true and the installation does not comply with EAWR, how does the installer comply with HASAWA Reg 3?Sorry you are getting confused about what it is the Regulations apply to.
To put it in simple terms, the ground does not have to comply with HASAWA.
If a worker then digs a hole in the ground, that task must comply with HASAWA.
Electricity does not have to comply with the EAWR.
How you use electricity when conducting a task for work must comply with the EAWR.
An installation in a building which is not used for work purposes does not have to comply with the EAWR.
How you use the electricity provided by that installation when conducting a task for work must comply with the EAWR.
An installation in a building that is a place of work, must comply with the EAWR.
How you use the electricity (irrespective of whether it is for a task of work) provided by the installation, must also comply with the EAWR.
Compliance with the EAWR can in many respects be achieved by compliance with BS7671.
there are two threads of conversation - the smaller one is about which earthing system you can connect to. I have pinched the typed up version of the reg but the answer is it has to be the same earthing system as the installation containing the protective device
"542.1.3.3 [...]if the protective conductor forms part of a cable, the protective conductor shall be earthed only in the installation containing the associated protective device."
there are two threads of conversation - the smaller one is about which earthing system you can connect to. I have pinched the typed up version of the reg but the answer is it has to be the same earthing system as the installation containing the protective device
"542.1.3.3 [...]if the protective conductor forms part of a cable, the protective conductor shall be earthed only in the installation containing the associated protective device."
but the argument is not about earthing the protective conductor, is it? it's about earthing the armour when said armour is not used as cpc.there are two threads of conversation - the smaller one is about which earthing system you can connect to. I have pinched the typed up version of the reg but the answer is it has to be the same earthing system as the installation containing the protective device
"542.1.3.3 [...]if the protective conductor forms part of a cable, the protective conductor shall be earthed only in the installation containing the associated protective device."
What installer?So if this is true and the installation does not comply with EAWR, how does the installer comply with HASAWA Reg 3?
Right now, I’m sat in my bungalow.Any installer anywhere.
Someone installed the work, and if they did this as part of a business, which we are discussing, not DIY, then the installation works and the requirement for compliance with EAWR of the installation was there when it was installed, thus the installer was required to comply with the law of the land as per EAWR & HASAWA.Right now, I’m sat in my bungalow.
I cannot (unless I look in a mirror) see any installers.
Why would my electrical installation have to comply with EAWR or HASAWA?
Ok, how about a supply to an outside socket or shed where you're coming from an existing socket on a RFC, plasterboard walls so you put in a single dry lining box for a DP switch or SFCU and drill through to outside behind the box, how do you earth the armour at that termination ? Yes I know you could terminate into a box outside but why create another unnecessary connection when you can earth the armour at the other end ? Or you could have an insulated CU to take your SWA from with no space around it for an additional connection box and no way of drilling a 20mm hole into it.
So you may end up with a metal consumer unit connected to a TT arrangement with a Zs of up to 1667 ohms for example, fitted adjacent to a metal adaptable box to which the swa is terminated with a Zs of perhaps .35 ohms. Is that right?
But it still doesn't say which ends it should be connected ....
Precisamundobut the argument is not about earthing the protective conductor, is it? it's about earthing the armour when said armour is not used as cpc.
If you are going to use that as an argument for earthing at both ends then you would have to apply the same argument to all radial circuit cpc's as damage may result in partial or complete loss of earth to part of the circuit.No it doesn’t say specifically which end of an SWA cable must be earthed if it is done at only one end, it says what must be achieved by the earthing. These regulations assume that we have enough sense to apply them correctly and don’t need a step by step guide to every little detail.
So the regulation basically says that the armour must be earthed to prevent it becoming charged (either through induction, capacitance or touching something which is live) in normal service or under fault conditions.
In normal service it wouldn’t matter which end is earthed, however under fault conditions such as physical damage it is possible that several armour strands could be broken. This could lead to the armour on the live side of the damage being unearthed if the connection was only made at the load end.
Exactly why high integrity earthin requires a second CPC.If you are going to use that as an argument for earthing at both ends then you would have to apply the same argument to all radial circuit cpc's as damage may result in partial or complete loss of earth to part of the circuit.
Not all scenario's are sufficiently likely to be worth allowing for.
Don't think earthing a cables conductive part is classed as requiring high integrity earthing.Exactly why high integrity earthin requires a second CPC.
My reply was in response to your statement about applying the argument to radials and damaged CPCs.Don't think earthing a cables conductive part is classed as requiring high integrity earthing.
I don't understand your argument here to be honest. You have got to gland the SWA to something have you not?? So just earth it at that point. I often use a Wiska box on the outside wall, not forgetting the danger 230V labelOk, how about a supply to an outside socket or shed where you're coming from an existing socket on a RFC, plasterboard walls so you put in a single dry lining box for a DP switch or SFCU and drill through to outside behind the box, how do you earth the armour at that termination ? Yes I know you could terminate into a box outside but why create another unnecessary connection when you can earth the armour at the other end ? Or you could have an insulated CU to take your SWA from with no space around it for an additional connection box and no way of drilling a 20mm hole into it.
I don't understand your argument here to be honest. You have got to gland the SWA to something have you not?? So just earth it at that point. I often use a Wiska box on the outside wall, not forgetting the danger 230V labelOk, how about a supply to an outside socket or shed where you're coming from an existing socket on a RFC, plasterboard walls so you put in a single dry lining box for a DP switch or SFCU and drill through to outside behind the box, how do you earth the armour at that termination ? Yes I know you could terminate into a box outside but why create another unnecessary connection when you can earth the armour at the other end ? Or you could have an insulated CU to take your SWA from with no space around it for an additional connection box and no way of drilling a 20mm hole into it.
No you wouldn’t, you can’t have exposed metal connected to two different earthing systems like that. You insulate the armour at the load end of the submain so that it does not introduce another potential.
Also leaving a TT system with such a high Ra is unacceptable.
I am fully understanding the situation, and this is not just my opinion it is that of many others, and other organisations.I think your problem is that you are confusing a ‘task of work’ with a ‘domestic installation’.
If no task of work is being conducted, neither the HASAWA or the EAWR applies.
If a task of work is being conducted the HASAWA and EAWR would apply to that task, not to the domestic installation.
It may be that the task of work is to make safe a dangerous condition in the domestic installation.
How would such a task be able to be conducted if the domestic installation must first comply with HASWA and the EAWR?
Reply to New sub board for shed swa advice. in the UK Electrical Forum area at ElectriciansForums.net