Hi All, Know this has been mentioned 1000s of times but here goes.
Customer would like NEW CU. Currently 16mm T/E 8m Run from Meter to CU.No Gas Bond,6mm water
I would like to fit 60a fused isolator , 10mm earths to gas and water and re use T/E. Think the CPC on T/E
is 6 or 10mm. The Max demand is low. A Colleague has apparently done this '100s of times'. I think that to
comply I need to run a 16mm earth from meter to CU ?
Any advice please
 
Where do the bonding conductors terminate ? MET near the meter with the earthing conductor or in the CU earth bar ?
 

Reply to NEW TAils or Not in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
850
Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU...
Replies
18
Views
1K
Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
410
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
570
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock